(OP)
I have been asked to comment on a concern with the construction of a lintel.  The lintels are 2 courses high. The bottom course is a precast concrete,4000 psi, U-block unit  with 1 #5 bar and the top course is a masonry unit, f'm =1500 psi, with 1-#5 bar. Type S mortar was used in lieu of 3000 psi grout for the reinforcing embedment.  Is there a way to calculate something like this or should I refer them to the precast concrete manufacturer's consulting engineer?  Thanks for any help.

RE: Mortar used in lieu of grout for precast concrete lintel

If the precast works by itself unfilled then you know you're ok no matter what.  The easiet thing to do is tear it out and make them do it right.  Are you the EOR or did they hire you to check it?  I would ask for tests of the the mortar to confirm its strength.  With that, you may be able to check the lintel as a masonry beam with the masonry code.  I can't imagine why on earth a mason would fill a precast with mortar.  They should know better.

RE: Mortar used in lieu of grout for precast concrete lintel

(OP)
Thank you for your reply, UcfSE.  You are right they should know better. I was hired by the masonry contractor to comment and provide calculations showing the strength of the as-built assembly.

RE: Mortar used in lieu of grout for precast concrete lintel

If a testing program will be developed for the mortar, compressive strength determination alone will not suffice since there are other forces in play. Bond strength is very important. Compared to the bond between grout and reinforcing steel, I am pretty sure the bond between reinforcement and mortar is very low.

RE: Mortar used in lieu of grout for precast concrete lintel

The precast lintel must be strong enough to carry the load above the opening by itself. There is no point in testing the mortar. There is no design method or allowance in any code I am aware of that allows for designing a bond beam using mortar instead of grout.
Regards.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources