ATEX explosionproof circuit
ATEX explosionproof circuit
(OP)
I am wiring a couple of ASCO Explosion Proof (ATEX EExd IIC IP67) solenoid valves. Two valves are mounted so the conduit connections are on a tee, with the third leg of the tee connecting into an explosionproof switchbox on a ball valve actuator.
My question is: Do I need to use sealed cable glands on all three legs of the tee? Or is one cable gland on the connection to the limit switch assembly code-compliant?
My question is: Do I need to use sealed cable glands on all three legs of the tee? Or is one cable gland on the connection to the limit switch assembly code-compliant?





RE: ATEX explosionproof circuit
If it is in Zone 1 with gas group IIA or IIB AND has an internal volume greater than 2 litres then it requires a barrier gland.
Otherwise a suitable flameproof gland with a sealing ring can be used.
Refer to EEMUA Publication 186 for some guidance - a useful document to have.
----------------------------------