weight of sprinkler systems

weight of sprinkler systems

weight of sprinkler systems

(OP)
I am away from my office; can anyone confirm 6 PSF allowance for water based sprinkler system?

Regards,
Lutfi

RE: weight of sprinkler systems

Past calcs I've done have come up at about 2.5 psf.  This was for a wet pipe system in a large warehouse.

RE: weight of sprinkler systems

Last time I was involved with sprinkler loads, was related to a pre-engineered building and they assumed 3 psf... same ballpark for wet system...

Dik

RE: weight of sprinkler systems

It's best to take a look at the piping layout, as some areas will be much more heavily loaded tahn others. Seems to me that the maximum I've found is 6 psf.  Wet pipe weights:

Dia.
1"   2.2 plf
2"   5.2 plf
3"   10.8plf
4"   16.4plf
5"   23.5plf
6"   31.7plf

RE: weight of sprinkler systems

I've just completed a school with a sprinkler system - on the advice of the supplier I included a UDL of 0.3kN/sq.m which is approximately 6 psf.

I would agree with jmiec however and examine the pipe runs - there are primary pipes which are larger diameter (and hence heavier loaded) than the smaller secondary runs.

RE: weight of sprinkler systems

Always look at the pipe runs, I hate to go out on a site visit and see a 9" diameter main running parallel to a typical K series bar joist.

OUCH!

RE: weight of sprinkler systems

(OP)
Many thanks to all. Based on my talks with Fire Protection Engineer and project layout, 6 PSF is a reasonable load.

Regards,
Lutfi

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources