I have 20 pipe lines of average lengths about 100 ft and dia of 2 in with liquid temp 150F to be freeze protected above 40F.Can i use one thermostat and have ambient set at 40F and switch all 20 heat tracing circuits(Self regulating heat tapes) from a powersupply panel?






RE: Heat Tracing
Generally if the tapes are self limiting then you could use an ambient thermostat physically located at the absolute coldest area you want to protect. You then control a handful of relays with the the thermostat which will in turn run the HTs.
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Heat Tracing
RE: Heat Tracing
Heat tapes are often de-energised in warm weather when they are not needed. The self regulating feature limits the maximum temperature but does not turn them off completely. You can waste a lot of energy trying to heat cold water a couple of degrees.
yours
RE: Heat Tracing
Otherwise, what you describe works OK with self-limiting cables.
RE: Heat Tracing
Thanks. That idea didn't strike me becuase the tracers I used, so far, are not for freeze protection but to heat fuel oil to boilers. Anyhow, it is right time for me to take some classes in lateral thinking
BTW, can you please let me know, what percentage of power we waste, once the fluid temperature reaches the set temperature of the tracers, on an average.
RE: Heat Tracing
I'm sorry. I missed the point of the fluid temperature at 150F
I should have said "You can lose some energy" rather than "A lot of energy"
I just did a little checking and found;
Self regulating tapes have a maximum temperature and a maximum de-energised temperature. The actual temperatures vary with the type, but 150F is dangerously close to the limit for some types.
The temperature/wattage curves do not go to zero wattage. The curves end at the maximum temperature and show a small output at maximum rated temperature.
If you can get some performance curves for the particular tape you are using you will be able to make a guess as to the losses.
The application instructions recomend using thermostats but self regulating tape may be used without thermostats.
rcwilson's warning concerning inrush currents is noted in the installation instructions for self regulating tape.
See
http://www.heat-trace.com/index.html
respectfully
RE: Heat Tracing
On previous projects, I ran a Windows program from the heat trace vendor that calculated heat loss at a minimum expected ambient temperature X in Y mph wind with a pipe with Z" of insulation with factor Ra to be maintained at b°C.
Are your pipes insulated? Have you calculated heat loss under assumed conditions? Is the self regulating tape of sufficient rating to make up the heat loss?
2) I'm not sure what you mean by 'freeze protected above 40F'. One is usually concerned about freeze protection below a certain ambient temperature, not above an ambient, like 40°F. Can I ask how you picked 40°F?
Dan
RE: Heat Tracing
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Heat Tracing
RE: Heat Tracing
I have seen caustic solutions in a waste oil reclamation facility that froze at a higher temperature than water. We used a freeze point temperature of 40 F. (I got the figure from the chemical dept. They may have added a few degrees safety factor to the actual freeze point but it was definitely above 32 F.) The heat tracing on the caustic lines was on our "watch" list in cool weather. In a batch operation, the fluid may be standing and cooling down at times.
respectfully
RE: Heat Tracing
Most ot the bunkerC i have seen traced was with steam trace. When the traceing system goes down it turns to roofing tar.
Second install current monitors to alarm on failure of the system. Some people use indicating light with signs to call someone if the light is out, but they never seem to. I am not up on the latest monitoring systems but I am sure there are some better ones out there.
RE: Heat Tracing
Excellent points BJC. I would certainly follow your suggestions.
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Heat Tracing
I just mention them in another thread on agitators but I don work for them or have stock in the company <%^)http://www.veris.com/