Bending Coefficient, Cb, for Allowable Stress Design
Say I want to really get nit-picky and use true Cb for a beam instead of using the standard conservative Cb=1.0.
When entering the beam curve charts, is it correct to enter using the value M/Cb instead of "Allowable Moment", or should I instead enter using (unbraced length)/Cb for hyperbolic portions of a curve (or Lb/(square root of Cb) for parabolic portions) instead of "Unbraced Length"?
I have always entered with M/Cb (similar to LRFD's Mu/Cb) and the unbraced length.  It is only recently where I have seen the Cb applied to the unbraced length itself.
Obviously, this question applies to ASD cases where Lb>Lu.
Thanks for any insight you can offer.
RE: Bending Coefficient, Cb, for Allowable Stress Design
The use of the two approaches compared with the closed form formulation of the check should confirm or deny the validity.
I don't believe that you can simply adjust your unbraced length or your moment capacity with Cb and enter the charts.  If you look at the equations F1-6, F1-7, and F1-8 you will see the following:
The break points for the charts depend upon the square root of Cb.
The allowable stress in F1-6 depends upon Cb used in a denominator added to 2/3 and therefore is not a direct linear relationship.
The applicable allowable stress in some cases is the larger of F1-7 and F1-8, therefore a direct adjustment linearly by Cb is not appropriate.
What you must do is use the equations and skip the charts.  They were developed only for Cb = 1.0.
Just as the triple lux may not win you the gold, this method will not necessarily provide you with the correct section.
This method is a good approximation, however the shape should still be checked per the applicable formulas from AISC chapter F.
The beam charts you speak of ARE NOT limited to use with Cb=1.0.  You CAN enter using Lb/Cb (in place of Cb) for hyperbolic curve portions or Lb/(Cb^(1/2)) for parabolic portions of the curve.  Obviously, once your size is selected (preliminarily from the charts), do your final check based on the equations F1-6 through F1-8.
Granted, Cb=1.0 is conservative and 99.9 percent of the time is what is used for expediency in design, but using real Cb is certainly not a prohibitive approach.  Using the charts with the "adjusted Cb's" mentioned above is a lot quicker than trial and error checks of beams from the Sx tables with Lb>Lu and real Cb.  The charts are the best starting point when Lb>Lu, whether Cb=1.0 or Cb>1.0.
Steel Structures: Design and Behavior", 4th edition, by Salmon and Johnson clearly addresses this topic. (Page 527 for those of you playing along at home.)