R507 system static pressure

R507 system static pressure

R507 system static pressure

(OP)
What is the typical “standby pressure” AKA “static pressure” range for a R507 refrigeration system at 70 degF?   Note: I am not using this information for charging the system.  The information is need for a rough transient analysis during startup.  

RE: R507 system static pressure

CRG
Depends upon your ambient temperature.

Best regards
pennpoint

RE: R507 system static pressure

(OP)
pennpoint, sorry I did not make myself clear.  What I meant by “static pressure” is when the AC system is deactivated (power disconnected) and has been off for some time.  In other words, when the pressure is the same everywhere in the system and with an average temp of 70 degF for all the AC’s components.

RE: R507 system static pressure

CRG
Then I repeat my reply: It depends upon your ambient temperature. There are look up tables for psi @ 70 F.

Best regards
pennpoint

RE: R507 system static pressure

The pressure will correspond to the hottest part of the system that contains liquid. The liquid will very slowly migrate to the coolest part of the system, or, at equal temperatures, the lowest part of the system. Very slowly. Hence crankcase heaters to keep refrigerant out of the oil in some systems with the receiver higher than the crank case. But usually, either of pennpoint's posts.
Look it up.
yours

RE: R507 system static pressure

(OP)
Thanks waross.  The point I missed is that all properly charged AC systems using R507 will have some liquid phased refrigerant condense in the coolest segment when the system is at static equilibrium.  I did not know for certain that there were no exceptions on the initial charge always including some liquid phase for all possible ambient temperatures.  

RE: R507 system static pressure

If you have a system with so much volume that all the refrigerant may vaporize when at rest the static pressure will be lower and will also depend on the volume of the system, but I do not know of such a system. In such a case the pressure will depend on the individual system design.
respectfully.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources