A 300mm2 shielded XLPE power cable has the following marking embossed on its outer sheath: 1.8/3(3.6)kV. What do the figures in this nomenclature mean?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Cable rating nomenclature
|
RE: Cable rating nomenclature
3 - denotes the phase to phase voltage rating
1.8 - denotes the phase to neutral voltage rating
(3.6) - extended rating? Im not quite sure about this.
GO PLACIDLY, AMIDST THE NOISE AND HASTE-Desiderata
RE: Cable rating nomenclature
3 - RMS Power Frequency voltage between phases of SUPPLY SYSTEM
(3.6) - Maximum rms power freq voltage between two phases for which cables are designed. This is the highest voltage that can be sustain at any time. This exclude transient voltages.
RE: Cable rating nomenclature