Jobs

Cable rating nomenclature

Cable rating nomenclature

Cable rating nomenclature

(OP)
A 300mm2 shielded XLPE power cable has the following marking embossed on its outer sheath: 1.8/3(3.6)kV. What do the figures in this nomenclature mean?

RE: Cable rating nomenclature

1.8/3(3.6)kV

3 - denotes the phase to phase voltage rating

1.8 - denotes the phase to neutral voltage rating

(3.6) - extended rating? Im not quite sure about this.

GO PLACIDLY, AMIDST THE NOISE AND HASTE-Desiderata

RE: Cable rating nomenclature

1.8 - RMS Power frequency voltage to earth of SUPPLY SYSTEM
3 - RMS Power Frequency voltage between phases of SUPPLY SYSTEM
(3.6) - Maximum rms power freq voltage between two phases for which cables are designed.  This is the highest voltage that can be sustain at any time.  This exclude transient voltages.

RE: Cable rating nomenclature

(OP)
So if the cable is new and were to be subjected it to an insulation resistance (Megger)test, would it be correct to set the tester to twice the phase-to-phase voltage rating of the cable (that would be 6kV)?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources