Hi All,
While I'm still very much learning about this subject, as I look in the standard, there's no talk of ground fault settings for breakers. Probably an ignorant question, but why?
Mike
While I'm still very much learning about this subject, as I look in the standard, there's no talk of ground fault settings for breakers. Probably an ignorant question, but why?
Mike






RE: Arc Flash/Ground Fault
In IEEE 1584, they state that three-phase faults should be used as the basis for arc-flash calculations. There are a couple of reasons for this:
Arc-energy release for three-phase faults should be the worst case.
Arcing faults that start as something tend to escalate (very quickly) to three-phase faults within equipment, due to the conductive plasma that forms.
So no matter what type of system grounding and ground fault protection you have, the PPE requirements are always based on the three-phase fault energy and phase protection (per IEEE 1584). I don't think NFPA 70E really specifies this one way or the other.
For outdoor substations, with the much greater spacing between phases, these assumptions probably don't make much as much sense. The Arc Pro software that is used by some utilties is based on line-to-ground faults, so I assume you can use the ground fault clearing times to determine the arc energy.
RE: Arc Flash/Ground Fault
RE: Arc Flash/Ground Fault
Thanks for that.
Mike