Fuel Gas Skid for Gas Turbine

Fuel Gas Skid for Gas Turbine

Fuel Gas Skid for Gas Turbine

(OP)
Hi Guys,

I'm currently involved with the cogeneration project. Now under construction phase. We're going to install 4 GTG and 1 STG. Our GTG got the supply of NG for the national grid.

Each GTG has its own fuel gas skid consists of filters, dual SSOV (safety shut-off valve) and pressure control valves.

My question, for the control valve is it common to have self regulated valve or instrument air (IA) regulated valve. Someone say if using IA, the risk of tripping the GTG is higher with the failure of IA supply.

Any feedback is appreciated

Thanks

norzul

RE: Fuel Gas Skid for Gas Turbine

We have lot sof turbines all of which use air regulated valves, you will probably find the turbine needs air anyway for other on skid instruments, purging on cooldown stop and all sorts of other reasons. self regulated valves in my opinion are just as likely to drift and fail as your instrument air supply.

If you are in a remote area and dont have an air supply, if your fuel gas quality is good you can even use instrument gas actuated valves. But I would check you dont need air anyway before using this as a reaon to go to self actiated PCV's.

RE: Fuel Gas Skid for Gas Turbine

Our gas skid valves are controlled with hydraulic oil.  This hydraulic oil comes from a gear driven pump and backed up with an AC-powered auxiliary pump.  We do NOT use IA to control the gas turbines.

RE: Fuel Gas Skid for Gas Turbine

toothless,

Are you describing the throttle valve arrangement, or the local pressure regulator? Our turbines - MW-701DA's - use a pair of electro-hydraulic servo valves in the throttle arrangement. One valve serves as the throttle, the other maintains a constant DP across the throttle to linearise the characteristic and additionally acts as the OST valve.

There used to be a local regulator driven by instrument air and controlled by a downstream PT via the DCS, but it was sluggish and troublesome. Its main function was to allow startup at a reduced gas pressure, but it caused more problems than it solved. It was scrapped and replaced by an altogether more reliable spool piece.

----------------------------------
  I don't suffer from insanity. I enjoy it...

RE: Fuel Gas Skid for Gas Turbine

(OP)
Dear All,

The link below will direct yu to my technical blog explaining the SSOV application. Appreciate your feedback.

http://technical2005.blogspot.com/

Thanks

norzul

RE: Fuel Gas Skid for Gas Turbine

We also use the instrument air  for the regulation of gas fuel valve.So far our CT has never tripped as a result of instrument air failure and i also  think probability of instrument air failure is no higher than failure of any other critical circuit in plant.Usually most facilities like us have standby compressors  and still if there is any failure then its better that the  gas turbine gets tripped as most of the  instruments in  the rest of the plant will stop responding as result of this failure .

The only concern which we have with using instrument air is Slow response of valves which sometimes cause the machine to overspeed whenever the generator breaker opens on any fault......

RE: Fuel Gas Skid for Gas Turbine

"...only concern which we have with using instrument air is Slow response of valves which sometimes cause the machine to overspeed whenever the generator breaker opens on any fault......"

I was recently ask to review a ST protection that used Pnuematics to trip SV.  the actuator had fast dump valves, but someone had decided to increase the local regulator from the required 30 psig need to open to 90 psig.  thus trip time increased geatly.  After reducing air to design, trip time went from many seconds to .2s

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources