I'm looking to locate hanging partition loads on my structural drawings but do not have specific information from the architect...go figure. The loads are being suspended from CFS trusses. What is a conservative design load to show on plan? My partition length is 30' so is it reasonable to specify say a 100plf and 3000 lb concentrated load anywhere along the track? Any suggestions?
TIA
TIA






RE: Folding Partition (Suspended) Loads
Typical loads range from 6-10 psf. 10' high partition = 100 plf on the high end of the spectrum. don't forget stacking loads and any other possible loading configurations.
RE: Folding Partition (Suspended) Loads
Dik
RE: Folding Partition (Suspended) Loads
RE: Folding Partition (Suspended) Loads
The load range that SperlingPE gave is typical.
RE: Folding Partition (Suspended) Loads
Also, don't forget that when the partition is folded up, ALL its weight is at one location - so two different load conditions need to be checked.