Construction Joints in Poured Walled
Why is that most structural engineers specify in their notes that concrete poured walls shalled not be poured more than 40'-0" (or close to that) in one single pour. Is this a curing issue? Does this need to be true in control joints are placed every 20'-0"? Thanks
RE: Construction Joints in Poured Walled
I’m a bridge engineer and in bridge applications we typically require a vertical construction joints every 25’ in an abutment or pier walls.
Please note that control joints are often not 100% effective (in relieving shrinkage stesses) since we often run either all the steel thru or cut every other bar. Even construction joints are not 100% effective especially when several days later the next section is poured (while the shrinkage is still happening).
Placing temperture and mix design have a major effect on concrete's initial set time and on shrinkage stresses.
Mary Hurd's book "Formwork for Concrete" has many good suggetions and details for concrete wall forming and placing, including a table of placement speed vs. formwork loading.
A 40' long section of 12" wall, 10' high contains 14.8 cy of concrete, which is basically two ready-mix truck loads. If it is placed at the rate of 5'/hr, then it takes 2 hours.
Placing stronger wall ties at the bottom section of the wall forms allows a faster pour rate.
Equipment makes a big difference in placing time too. Is the concrete placed by chute directly into the forms, with a pump or bucket or conveyor?