Circuit Breaker Question
Circuit Breaker Question
(OP)
I believe this was inapropriately posted in Electric Motors and Motors Control Engineering so I am reposting it here.
FORGIVE ME FOR DOUBLE POSITNG!
I have a customer asking for assistance with selecting the correct main circuit breaker for a 10HP 460V triplex vacuum system. Depending on the demand, only one unit could be in operation or all three could be operating at the same time. Motor FLA is 14 each (w/0 1.15 SF).
Cutler Hammer Motor Circuit Selector says the following:
1. Instantaneous trip circuit breaker GMPC/HMCP: 30 AMPS and
2. Circuit breaker trip rating: 35 AMPS
A.) Can someone provide a briefly explain the difference between #'s 1 and 2? and
B.) Should the breaker be sized based on all three units in operation (10HP x 3 = 30HP)?
Just trying to help a guy out!
Thanks!
FORGIVE ME FOR DOUBLE POSITNG!
I have a customer asking for assistance with selecting the correct main circuit breaker for a 10HP 460V triplex vacuum system. Depending on the demand, only one unit could be in operation or all three could be operating at the same time. Motor FLA is 14 each (w/0 1.15 SF).
Cutler Hammer Motor Circuit Selector says the following:
1. Instantaneous trip circuit breaker GMPC/HMCP: 30 AMPS and
2. Circuit breaker trip rating: 35 AMPS
A.) Can someone provide a briefly explain the difference between #'s 1 and 2? and
B.) Should the breaker be sized based on all three units in operation (10HP x 3 = 30HP)?
Just trying to help a guy out!
Thanks!






RE: Circuit Breaker Question
yours
RE: Circuit Breaker Question
For a main breaker, you will want a standard thermal-magnetic breaker.
RE: Circuit Breaker Question
Thanks for responding.
The possibility that all three units could start at once does exist.
RE: Circuit Breaker Question
All three motors can be supplied from a common feeder. The circuit size for three motors would be 14 * 1.25 + 14 + 14 = 45.5 amps. The NEC allows the overcurrent protection for the feeder to be sized at a maximum of the sum of (the permissable overload protection for the largest motor) + (sum of the full load currents for the other motors). Got all that? It's somewhat complicated and should be evaluated by a licensed engineer.