Canned Pump Protection (Electrical)
Canned Pump Protection (Electrical)
(OP)
We are specifying canned pumps for several services in the near future. We are discussing (read: arguing) about the various protection levels for the pumps.
Options:
1. Temperature switch in the bearings and/or windings. We will be using this as I believe this is a standard.
2. Level switch. This is new to me. It is said that the pumps need to verify that it is full before being started. Any comments?
3. Power Switch (low and high). I've installed these on Mag pumps, but not canned pumps. The mechanical engineer requested power switches on canned pumps now also, but I'm not sure I agree. Essentially these will be in the 10-20hp range.
Are there any standards out there to indicate what protection is needed on a canned pump?
Options:
1. Temperature switch in the bearings and/or windings. We will be using this as I believe this is a standard.
2. Level switch. This is new to me. It is said that the pumps need to verify that it is full before being started. Any comments?
3. Power Switch (low and high). I've installed these on Mag pumps, but not canned pumps. The mechanical engineer requested power switches on canned pumps now also, but I'm not sure I agree. Essentially these will be in the 10-20hp range.
Are there any standards out there to indicate what protection is needed on a canned pump?
______________________________________________________________________________
This is normally the space where people post something insightful.





RE: Canned Pump Protection (Electrical)
I think we may have a some regional disparities of terms. I think I understand your terms but it is prudent to verify our terms.
By "canned pump" do you mean submersible pump?
What is a "Mag pump"?
What does the "power switch" do? Is it applied to a two speed motor?
Thanks
yours
RE: Canned Pump Protection (Electrical)
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Canned Pump Protection (Electrical)
htt
RE: Canned Pump Protection (Electrical)
Thanks stardelta.
Keith Cress
Flamin Systems, Inc.- <http://www.flaminsystems.com>
RE: Canned Pump Protection (Electrical)
For now, here is what I have to offer:
1) Temperature protection is often used to supplement the Overload Relay in pumps because there are some conditions that may end up heating up the pump long before the motor draws more current. Those conditions can be loss of prime, blockage, seal failure, bearing failure etc., all dependant on the type of pump of course because not all of these issues are problems on every type of pump. Thermistors are the most popular supplemental protection devices right now on pumps that size, but they need a Thermistor Trip Relay in the control circuit. Kilxon snap action thermostatic switches are still the cheapest however.
2) Many pump designs cannot run without fluid in them, others can run dry virtually forever. That is strictly a design issue with the pump. Another alternative to level detection protection is to use a current sensing relay to determine when the pump in running dry, and often the most critical designs use both.
3) Still don't know what you mean by the Power Switch, but if by "canned pump" you mean a canned pump station where the pump tank and housing are sold as a unit, then maybe you mean the disconnect switch? I don't know how the "low and high" would fit with that though.
Eng-Tips: Help for your job, not for your homework Read FAQ731-376
RE: Canned Pump Protection (Electrical)
RE: Canned Pump Protection (Electrical)
MAGNETIC PUMP:
A magnet is attached to the shaft. An electric motor turns some magnets outside of the can and the magnetic field is transferred to the magnet inside the "can" causing it to turn. The magnets are covered with a corrosion resistant covering.
Power switch "looks" at the power draw on the leads to the motor. The Low/High is Underpower (which would indicate dry run)/Overpower (overload: can be taken care of with the motor heaters)
______________________________________________________________________________
This is normally the space where people post something insightful.
RE: Canned Pump Protection (Electrical)
By the term usage we are used to, the Stator, by definition, is stationary. I think you meant to say rotor, which by definition, rotates.
Other than that, you seem to know more about this field than most of us.
A couple of comments based on general experience.
If the motor is depending on the circulation of pumped fluid for bearing lubrication and/or cooling, a level switch may be wise.
Power switches, (Load monitor?). If the mechanical engineer wants it, he may know something about the process that you don't.
Politically, if someone is making a stand on a protection issue, it is not always wise to oppose too strongly. If there is a consensus that a particular device will protect against a 1 in 10,000 event and can be dispensed with, a subsequent 1 in 10,000 failure can be accepted and forgiven.
If someone has taken a very strong stand, been overruled, and the 1 in 10,000 event occurs there is sure to be finger pointing, "I told you so's", and not much forgivness.
It may be a time to ask and listen rather than to argue.
respectfully
RE: Canned Pump Protection (Electrical)
Another 'feature' that can surprise the unwary; all the waste heat from the motor goes into the pumped fluid.
Mike Halloran
Pembroke Pines, FL, USA
RE: Canned Pump Protection (Electrical)
http://www.chempump.com/
Very $$$
Best regards
pennpoint
RE: Canned Pump Protection (Electrical)
RE: Canned Pump Protection (Electrical)
Thanks controlnovice
respectfully
RE: Canned Pump Protection (Electrical)
Pumps typically need to be protected against dry running and cavitation. This can be done by the use of level probes to check the fluid level and a flow switch to ensure that there is continuous flow. It is common for the installation to be protected against a broken pipe by the use of a minimum pressure switch. It is also common for an over pressure switch to be used to protect agains pump deadheading (closed valve on the output).
Under current protection against a dry pump or closed valve is only partially effective due to the current variation with voltage. Shaft power monitoring will give a higher level of security against dry run, cavitation and broken pipe than current based monitoring.
Best regards,
Mark Empson
http://www.lmphotonics.com
RE: Canned Pump Protection (Electrical)
I learned that the temperature switch is not in the bearings. All canned pumps I've ever installed had a temperature switch in the bearing (sometime referred to as bearing wear detectors)...just not these. These temperature switches are installed in the windings to obtain the Explosion Proof rating for the pump/motor.
The level switch is also used to verify the pump is full. I am told that this is also to maintain the pump/motor's explosion proof rating. If it is full of liquid (no air), then there is not an explosive atmosphere. Since the liquid is pumped through the stator/rotor, I can see this, but it makes more sense to me that it is there to prevent starting when dry.
So, that leaves the power monitor (Load or kW Monitor), which is used to prevent run dry.
Whew....maybe I am learning something....my brain hurts.
______________________________________________________________________________
This is normally the space where people post something insightful.
RE: Canned Pump Protection (Electrical)
Eng-Tips: Help for your job, not for your homework Read FAQ731-376
RE: Canned Pump Protection (Electrical)
RE: Canned Pump Protection (Electrical)
Eng-Tips: Help for your job, not for your homework Read FAQ731-376
RE: Canned Pump Protection (Electrical)
Not necessarily for explosive atmospheres market.
More for any material (usually nasty) that the user want to keep contained. The canned pumps are seal-less and leak-proof. This is the main reason for canned pumps.
______________________________________________________________________________
This is normally the space where people post something insightful.
RE: Canned Pump Protection (Electrical)
RE: Canned Pump Protection (Electrical)
rmw
RE: Canned Pump Protection (Electrical)
You may end up canned with your canned pumps.
Best regards
pennpoint
RE: Canned Pump Protection (Electrical)
12 fish
As iron sharpens iron, so does a man sharpen the countenance of his friends
RE: Canned Pump Protection (Electrical)
Don
RE: Canned Pump Protection (Electrical)