a diode is needed ?
a diode is needed ?
Hi, I'm actually a computer enginneer and not an expert in electronics or electricity but I've done some applications involving relays before.
I used to work with 12V input relays(normal ones, not solid states), that usually required a diode in the circuit to prevent undesired voltage/current problems.
Currently I have a project in which I have to use 120V/220V input solid state relays, and I wonder if I still need to add a diode to the circuit in order to prevent electrical problems.
Thanks in advance.
Thanks in advance.
RE: a diode is needed ?
Solid state relays(SSR) are fully electronic.
Electromechanical relays have inductance that generates damaging kick-back when the coil is de-energized and so requires a diode often.
Just look at the SSR data sheet and hook it up that way. Pay particular attention to the de-rating curves!!
Remember too that most SSRs have leakage due to their output snubbers. This causes a lot of confusion in the field because they look like they are still on when checking them with a sensitive Digital Multi Meter(DMM). Often you need to use something like a lamp to shunt this leakage current to get "logical" readings.
Keith Cress
IF that input is coming from a triac (a triac output in a PLC or a triac output in a PID temperature controller), then you may need a burden resistor. This is to eliminate false turn ON due to triac leakage.
If that input is coming from a different location, such as a limit switch, then no burden resistor is usually required.
Do you switch the control VTG with switch of with electronics ?
Plesae read FAQ240-1032
WEB: <http://geocities.com/nbucska/>
The problem is that I want to detect if an air conditioner is turned-on at a given time.
I've make a diagram of my problem here:
http://www.regalos-especiales.com/SSR_diagram.JPG
Mike2468 : does this circuit needs the resistor you were talking about? if so, where should the resistor be connected, and also where should it be connected?
If you are using a PC to turn on the SSR you don't need a resistor.
I am having a problem with your power..
I would think that you have two hot wires and a safety ground running to the air conditioner. You would need to put the SSR in one of the "hot" wires NOT the safety ground.
I guess I am confused by the +,+,- expecting +,-,+.
Also you better make sure that is a hefty SSR because you have it starting a compressor (tough starting load). Remember that the SSR must get cooling!!! Or it will fail.
Keith Cress
simplest is to use an optocoupler OC ( LED & photo-transistor type)
Put a series R into the AC line which causes nominally
about 3V drop. rectify this with a four diode bridge.
The output diagonal of the bridge is connected to the
LED of the OC with a 200 ohm series resistor. Connect
a 5V zener parallel with this disgonal to reduce the start-up current surge.
A small Current Transformer in the line to the air conditioner will give a voltage output when the A/C is running that you can use to control the SSR.
You can use nbucska's circuit on the output of the Current Transformer.
A series resistor should be rated with consideration for the Stalled Rotor Current of the Air Conditioner. (Locked Rotor Current times the time for the thermal overload to open)
With 10 amps and 600% Locked Rotor Current your 3 volts will become 18 volts under stalled rotor conditions. At 600% of 10 amps that's 60 amps times 18 volts for a few seconds.
That's a little over a Kilo Watt. You may not find a suitable resistor at Radio Shack.
respectfully
I would just like to clarify something, Your second post reads "The problem is that I want to detect if an air conditioner is turned-on at a given time." but your diagram appears like a control device.
Chuck
Also just out of curiosity what software are you using for you program?
Kenneth H Boggs
Since the AC represents an almost costant load, the simplest would be a current transformer -- diode bridge--
clamping zener and optional filter cap i.e. up to 7 components
Keith Cress