Consider this list compiled from various county and UBC requirements a few years ago:
STRUCTURAL: ROUGH WOOD FRAME:
Verify wall sill (sole, foundation) plate anchor bolt size(s) and spacing.  Reviewed Plan details and UBC 1806.6.
Verify exterior wall sill (sole, foundation) plates are treated or Foundation redwood.  UBC 2306.4.
Verify the installation of all holdowns, straps and “hurricane” ties.  Reviewed Plan details and UBC 1605.2.3.
Verify the location, panel size, and nailing pattern of interior plywood or OSB shear walls.  Reviewed Plan details, UBC 1605.2.1 and UBC 1605.2.2.
Verify the location of required blocking for drywall (gypsum board) shear walls with the Reviewed Plan Shear Panel Schedule.
Verify required drywall (gypsum board) backing and support.  UBC 2511.2.
Verify the size of all structural members, i.e. beams, posts, girder trusses, rafters, joists, etc with the Reviewed plans and details.
Verify post and beam connections. UBC 2314, 2318, Reviewed plans, and details.
Verify the bearing load path(s) to insure all loads are properly supported from roof to the foundation.  UBC 1605.2, Reviewed plans and details.
Verify cutting, notching, and boring of wood members is not in excess of that permitted.  UBC 2316.3.2.3.2, 2316.3.4.4, 2320.11.7, 2320.11.9, 2320.11.10, 2320.12.4,
Verify top plate joints, ends, and splices are properly supported, lapped, and/or strapped.  UBC 2320.11.2.
Verify approved structural materials have been used, including grade stamps on lumber, sheathing, and engineered trusses.
Verify solid support (blocking / backing) at air vent terminals.  Support is required on the sides fasteners will be installed to mount the air registers.  Where a register may be installed or rotated in different positions, support is required on all sides.  UMC 1004.
Where rafters are installed, verify the rafters are framed directly opposite each other at the hip & ridge, the ridge board is not less in depth than the cut end of the rafter.  Hip and valley rafters shall be minimum 2 inches nominal in thickness and not less in depth than the cut end of the rafter.  UBC 2320.12.3.
Verify rafter ties are installed when required. UBC 2320.12.6.
Verify rafter and joist blocking.  UBC 2316.2 Amendment #18 (4.4.1.1), and #19 (4.4.1.2), 2320.12.8.
Verify the location of readily accessible access(s) for attic spaces 30 inches or more in height.  The access opening(s) shall be minimum 22” X 30”, or of sufficient size for the largest piece of mechanical equipment to be removed, and  shall provide a minimum of 30 inches clear headroom.  UBC 1505.1, UMC 307.3.
Verify the required attic, and under floor ventilation is installed.  UBC 1505.3.
Verify a free flow of air will be maintained when eave or cornice vents are installed.  UBC 1505.3.
Verify a minimum 1 inch air space will be maintained between insulation and the roof sheathing. UBC 1505.3.
Verify fire blocking in the following locations, UBC 708.2.1:
In concealed and furred spaces of walls at the ceiling and floor levels of combustible construction.
At 10’ wall intervals both vertical and horizontal.  Note, 8’ intervals may be considered when it is necessary to provide backing for plywood, OSB, drywall (gypsum board), or wall lateral bracing.
At all interconnections between concealed horizontal and vertical spaces, (i.e. soffits, drop ceilings, cove ceilings).
At the top and bottom of stair stringers.
Between studs along and in line with the run of stairs for unfinished walls below the stairs.
In openings around vents, pipes, ducts, chimneys, fireplaces, and openings at ceiling and floor levels.
At openings between attic spaces and chases for factory built chimneys.
Verify fire blocking material and construction, UBC 708.2.2:
Nominal 2X wood or equivalent thickness of 1 inch wood blocks.
2 layers of minimum 1/2 inch OSB.
Tightly packed fiberglass insulation.
Minimum 1/2 inch drywall (gypsum) board.
Other materials approved by the Building Official.
Verify gable end bracing in accordance with the Reviewed plan detail(s).
Verify a minimum finished ceiling height of 7 feet 6 inches in habitable spaces will be provided.  UBC 310.6.1.
Verify a minimum finished ceiling height of 7 feet in kitchens, halls, bathrooms, and toilet compartments will be provided.  The rough frame measurement from the floor to the ceiling joists or trusses is generally 7 feet 1 inch.  However, adequate space must be allowed for flooring and ceiling materials.  UBC 310.6.1.
Verify foam plastic insulation is not exposed to the interior of the building.  UBC 2602.4
TRUSSES
Provide the truss layout diagram and engineered truss calculations from the manufacturing company.  Truss calculation sheets and drawings shall be stamped and signed by a registered engineer of your State.
Verify the truss manufacturing company is legibly identified near the center on the bottom chord of each truss.  UBC 2321.4.
Verify the required truss lateral (web) bracing is installed in accordance with the manufacturer’s design shown on the truss calculations.
Verify any special truss blocks (bearing blocks, wedges, etc.) are installed in accordance with the manufacturer’s design shown on the truss calculations.
Verify the required truss hangers are installed in accordance with the manufacturer’s design shown on the truss calculations and/or the Reviewed plans/details.
Provide an engineered repair detail for any truss modified or repaired.  Verify modifications or repairs are installed exactly as required in accordance with the engineering.
Verify the roof is uniformly loaded to allow trusses to properly deflect.
Verify proper clearance (min. 1/2 inch) between non-bearing walls and truss chords.
Verify all truss bearing points are blocked and fully supported with the minimum bearing required by the truss calculations.  UBC 2320.12.8.
SHEAR:
Verify sill (sole, foundation) plate anchor bolt size(s) and spacing at exterior and shear walls.  Reviewed Plan details and UBC 1806.6.
Verify exterior wall sill (sole, foundation) plates are treated or Foundation redwood at exterior walls.  UBC 2306.4.
Verify the location, panel size, and nailing pattern of shear walls.  Reviewed Plan details, UBC 1605.2.1, 1605.2.2, 2319.
Verify nails and/or fasteners
Verify the size of all structural members that will be covered or hidden when the weather barrier, lath, and/or roofing paper is installed, i.e. beams, posts, girder trusses, etc with the Reviewed plans and details.
Verify approved structural materials, including grade stamps on lumber, sheathing, and engineered trusses.  UBC 2303
Verify the fasteners used with treated wood or exposed location are corrosion resistant and proper gage.
ROOF:
Verify approved structural materials, including grade stamps on lumber, sheathing, and engineered trusses.  UBC 2303.
Verify the roof sheathing size and span. UBC 2312.2, 2320.12.9, Reviewed plans and details.
All roof sheathing shall run perpendicular to the framing members and shall span a minimum of two spaces.  UBC 2320.12.9.
Verify truss and roof sheathing blocking and edge supports as required.
Panel edges 12” wide or less require minimum 2x4 solid blocking applied with the narrow edge for support.
Panel edges over 12” to 16“ wide require minimum 2x4 solid blocking applied with the wide edge for support.
Panel edges over 16” to less than 24“ require minimum 2 panel edge clips for support.
Reference UBC Table 23-II-B-2, APA Technical Report Number R275, Reviewed plans and details.
Verify the roof sheathing nailing pattern.  The standard nailing pattern for non-engineered roof sheathing panels is 8d’s nailed 6” O.C. at edges and 12” O.C. in the field.  UBC 2318, 2320.12.8, 2320.12.9, Reviewed plans and details.
Verify a gap (1/8” to 1/4”) is provided between roof sheathing panels to allow for expansion and contraction.  Refer to the manufacturer’s recommendations or installation requirements. (plywood clips)
Verify minimum roof slope for drainage.  Follow the approved plans (which may include engineered recommendations) where greater slopes are shown.  UBC 1506.1.
Collar and wall ties per code
boo1,
I thought you may have been the original author of the thread, but could not remember.  In any case, thank you.