Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login




Remember Me
Forgot Password?
Join Us!

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.
Jobs from Indeed

Link To This Forum!

Partner Button
Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

tito103 (Electrical) (OP)
15 Mar 06 17:46
Hello,
 I was infrared scanning a 2000 amp service 480 volts. The cables ran from a 2000 amp transfer switch too a 2000 amp main circuit breaker. The feeders are in cable and installed in cable tray. Approximate cable length 80ft. There where 5 parallel 600mcm feeders per phase.The problem I was having is a couple of the feeders  are drawing twice the current then the other feeders in the same phase? Does this mean that the cables drawing less current have a higher contact resistance?
itsmoked (Electrical)
15 Mar 06 18:01
Or maybe your meter is suspect?  Twice the current is um... a lot!

Keith Cress
Flamin Systems, Inc.- <http://www.flaminsystems.com>
dpc (Electrical)
15 Mar 06 18:21
Did you use a clamp-on ammeter to measure the current?  

And what did the thermograhpy show?  
tito103 (Electrical) (OP)
15 Mar 06 18:36
I noticed a 40 degree rise between cables. I clamped on my meter and noticed one cable had approx.560amps, the other four cables  had approx 200 amps. The swichgear current meter was showing around 1300 amps total current per phase so the total current reading makes sense. This is happening on all three phases.
wareagle (Electrical)
15 Mar 06 19:25
I had this problem before with compression bolt connectors.
Remove the hi current connector and brush and clean it. It probably has a higher resistance connecton.
wareagle (Electrical)
15 Mar 06 19:27
Let us know what you find.
dpc (Electrical)
15 Mar 06 19:34
It's possible for contact resistances and other factors to cause some surprising differences in current.  The problem can be worse in shorter feeders.  

You might also want to verify that the cables are basically the same length and are routed in a similar fashion.  
tito103 (Electrical) (OP)
15 Mar 06 20:17
I am waiting for a shutdown schedule. This is a critical load feeder. I will post results after shutdown. Thanks for the info!
Helpful Member!  waross (Electrical)
15 Mar 06 20:50
One couple of observations.
First
 

Quote (wareagle):

I had this problem before with compression bolt connectors.
Remove the hi current connector and brush and clean it. It probably has a higher resistance connecton.
This is entirely possible. I would check the connections.
On the one hand, I have had problems with clamp-on meters being affected by strong fields from adjacent cables, BUT I understand that you detected a temperature difference between the cables and your total currents correlate well with the switch board meter.  
With that much difference in current a bad connection would be developing heat. If you were infared scanning you may have noticed it.
On the other hand, it is possible that there is an impedace problem upsetting the distribution of current. This conclusion is supported by the fact that you did not report overheated connections and by your report that one cable in each phase is overheating.
How are the cables arranged in the tray? Improper phase arrangements in cable trays can cause unequal, division of currents.
I'd give it about 50/50 between bad connections and impedance problems due to improper cable arrangements.
You may want to try disconnecting the overloaded cable to see if the currents remain balanced on the other phases.
yours
itsmoked (Electrical)
15 Mar 06 20:53
I would expect warmer connectors at one or both ends of the lower amp cables.  Do you see this?

What kind of structure do the cables terminate on?  A buss bar? ?

Keith Cress
Flamin Systems, Inc.- <http://www.flaminsystems.com>
Helpful Member!  davidbeach (Electrical)
15 Mar 06 20:57

Quote (wareagle):

Remove the hi current connector and brush and clean it. It probably has a higher resistance connection.
Nope.  Just the opposite, high resistance connection would lead to low current.  Somehow one cable has significantly lower impedance than the other four.
Are the five runs identical in geometry?  Are the conductors grouped in groups of three with one of each phase in each group?  Is there any magnetic material that forms a loop around some of the conductors but not all of the conductors?  Something is very wrong, and given four lower current conductors and one higher current conductor, I would concentrate on the geometry of the installation, including all hangers and appurtenances and leave the connections for later.  (If it were four higher current and one lower current conductor I would immediately go after the connections on the lower current conductor, but to say that 80% of the connectors are suspect is a bit too much.)  Include the configuration of how the conductors exit the transfer switch and enter the main breaker enclosure in your analysis of the geometry of the situation; are there an equal number of conductors of each phase in each hole?
tito103 (Electrical) (OP)
15 Mar 06 21:35
Hey Guys, just for the record the equipment is pushing 35 years. I know another testing company had scanned this equipment 4 years ago, and did not mention anything about this in there report. Another thing I noticed they bunched all the same phases together on the cable tray. The cable is tied down with plastic tie-wraps. The fields are not interupted with any ferrous material. And the cables enter the enclosure in one large rectangular slot.
waross (Electrical)
15 Mar 06 21:40
Hello tito103
Bunching each phase together is probably the cause of the unbalance.
yours
wareagle (Electrical)
15 Mar 06 23:37
david beach
Thanks for that correction. I thought about it some time after the post and realized what I had said. You need to check the low amperage connector.
davidbeach (Electrical)
16 Mar 06 1:34
So you have 15 individual conductors, five each of three phases, plus any neutral and ground conductors; and for those 15 conductors, there are three bundles, each with five conductors of the same phase.  Is that correct?  And in one of those phases, one conductor is carrying 560A while the other four are each carrying 200A, for a total phase current on that phase of 1360A.  Is that also correct?  Which phase are these readings from?  What are the currents in the individual conductors of the other two phases?

The cable inductance would be lower if the cables were grouped such that each group had one conductor of each phase, plus a neutral if there are also neutrals.  The segregated bundles will have a higher inductance, and therefore a higher total impedance, but unless each bundle very carefully maintains its configuration within the bundle the entire run, each conductor should have nearly identical impedances, a 5% difference in cable impedance would be extremely high and no where near enough to cause what you are seeing.  I would expect more difference in impedance due to differing lengths of conductors than from geometry.  On the other hand, if the configuration is maintained with absolute consistency, you might get a noticeable difference between the inner edge of a bundle, where it is nearest to the bundle of an other phase than the outer edge, where there is no adjacent phase.  But even that wouldn't be enough for more than a few 10s of amps difference if it could even be that much.  Certainly not what you are describing.

You say the installation is pushing 35 years of age; I suppose it is possible that connections could be going bad, but I'd feel a whole lot better about that possibility if you had five different readings spread randomly across the 200A to 560A range, rather than four at the low end.

There is something very wrong here, and it is difficult to come up with anything that seems reasonable without a lot more information.  No promise that any reasonable suggestion come from further information, but the information will certainly help.
itsmoked (Electrical)
16 Mar 06 2:23
How about some pictures middle, ends?
They would be pretty useful at this point.

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
waross (Electrical)
16 Mar 06 8:05
Good morning davidbeach;
I understood from the OP's second post that the problem was similar on all phases.
I keep thinking that this sounds backwards. If the bundles were consistent we would expect fairly even currents except for the conductor in the center of the bundle which would have a LOWER current because of skin effect, not HIGHER.
I am wondering if this installation may be;
One bundle A-A-A-A-B, one bundle B-B-B-B-C, and one bundle C-C-C-C-A.
Comments?
BTW congratulations on regaining you customary position on the MVP list. Your quality has overtaken my quantity as it should.
respectfully
PWR (Electrical)
16 Mar 06 9:30
I have seen this problem on many installations.  It occurs due to unequal reactance when the conductors are randomly place in the tray and when they are neatly installed with all the phases grouped together.  The latter insures the worst case scenario.  As an example I documented some years ago:

40 inch wide tray, 7 - 500kcmil per phase (21 conductors total) arranged (from the source) left to right 7 - A then 7- B then 7 - C conductors.   Using a clamp on ammeter the C phase conductors (from the source) read 730, 350, 230, 185, 165, 220, and 410 amps respectively left to right.  Note that the left most conductor has the lowest reactance because it has the most flux linkages from the A and B phases and therefore carries the largest current.
davidbeach (Electrical)
16 Mar 06 10:00
PWR, your numbers make a whole lot more sense than tito103's numbers.  My guess is that you also had a run that was a whole lot longer than 80ft run considered here.  I would not have expected as much variation between high and low conductor, but enough length of run could make that happen.
PWR (Electrical)
16 Mar 06 11:04
Actually, the run I documented above was only about 30 ft total length.  The length only has to be long enough to establish a significant difference in the total impedance of each conductor.  The current is going to divide based on the difference in the impedances even if the total impedance magnitude is quite small in each conductor.
davidbeach (Electrical)
16 Mar 06 15:26
PWR, you're right, the current in a segment of the circuit would divide inversely proportionally to the relationship of the impedances of that segment.  I was mentally comparing the conductor impedances with the rest of the system impedance, but that was not correct.  Sometime when I've nothing better to do (not any time soon unfortunately) I'll try to remember to do some modeling on this, I'm intrigued that you could get that much difference to have over three times the impedance on one conductor as on another.

None of that changes the fact that I don't like (can't make sense of) tito103's numbers; if they had a whole lot more spread to them they'd make much better sense.
waross (Electrical)
16 Mar 06 16:47
Hello davidbeach
You seem to have missed my post of 16 Mar 06 8:05, or more likely we were posting at the same time.

Quote:

I am wondering if this installation may be;
One bundle A-A-A-A-B, one bundle B-B-B-B-C, and one bundle C-C-C-C-A.
Comments?/
I think this arrangement may explain the unusual division of current.
tito103, Can you check and see if the cables are in fact arranged similar to this?
Thanks.
respectfully
davidbeach (Electrical)
16 Mar 06 17:12
waross, I saw that post, but read it as laid out flat in the bottom of the tray.  Without doing any modeling, it seems to me that your configuration (laid out flat in a tray) would provide at least three different currents, and probably a spread more like what PWR reported on his measurements.  If you mean bundle as with tie wrap around each bundle and wide separations (wide as compared to cable diameter) between bundles, maybe, but best to hope that the high current cable is on the top of the bundle or there will be serious heating problems.

What we really need now is for tito103 to respond with much more information than he (she? - just can't tell with most handles) has provided to date.
tito103 (Electrical) (OP)
16 Mar 06 21:50
hey guys, the cables are placed like this.
  cccccbbbbbaaaaannnnn the width of the tray. None of the cables are stacked on top of each other, and they are all tie-wraped to the tray individually.
waross (Electrical)
16 Mar 06 22:31
Thanks tito103.
I agree with davidbeach and PWR. Those readings don't make sense. The high current is to be expected. The low currents being equal is not normal. When you say "the other four cables  had approx 200 amps.", do you mean within 5%, 10% 20%?
I am thinking about an ammeter I had once that misbehaved badly when exposed to the magnetic fields of surrounding conductors.
I had another ammeter that had a habit of sticking mid scale when static built up on the face. That made a lot of readings look equal that actually weren't. It wasn't particularly accurate either.
Is it possible that one set of 600 MCM cables is really 750 MCM?
I would not normally make such suggestions but these readings do not seem to be a normal.
respectfully
davidbeach (Electrical)
16 Mar 06 22:54
tito103, you should have five different current measurements per phase based on that configuration.  What about the currents in the other two phases and neutral?  Have you physically inspected the entire run and found that nothing comes between the conductors at any point; any metallic clamps, any all thread hanger rods, anything?
KJvR (Electrical)
17 Mar 06 8:19
tito103,

My first thought was also due to the unsimmetric cable lay-out, but your currents would have varied as already stated.  My second thought was that your cables have screens and maybe one of the screen connections was bad, causing additional unbalance.  Although you can get such high variances in current, it still does not explain why it happens on all three phases and the other cables' currents are more or less the same at 200 A.

I would like to support the idea of a different set of cables (raised by warros).  The installation is already 35 years old and expansions surely must have happened.  An additional cable could have been installed and it might be that a Cu conductor in stead of an Al conductor was installed or just a different size cable.

KJvR
tito103 (Electrical) (OP)
17 Mar 06 18:11
Hey guys great info! as far as the cable placement, there is only one row of cables. None of the cables are placed on top of each other. They are straight across the cable tray. I checked all the cables and they are all copper 600mcm. As far as ferrous clips or supports there are none.  The only supports are plastic tie wraps. During an infrared inspection I picked up on this problem. The first thing I did was amprobe the conductor with the most heat, that was the cable with 560 amps. The cable terminated next to it was drawing about 200 amps and looked normal during the infrared inspection. I could not take current readings from all the cables because it was to dangerous. Hope this info is a little more helpful.
waross (Electrical)
17 Mar 06 19:27
Thanks for the clarification tito103
As you realised we were under the impression that the currents had been measured in each cable. The situation is not good but is to be expected with that cable arrangement.
The Canadian Electric Code recomends ABCABCABCABCABC for parallel feeders laid flat in a cable tray. What says the NEC fellows?
You have a good case for some remedial work reconnecting the cables in an approved or recommended configuration on the next scheduled shutdown.
respectfully
matwong (Electrical)
20 Mar 06 3:38
What I suspect is the connection problem at your terminals of transfer switch or MCCB.  I presume the cable carries the highest current is connected directly to the terminals of the equipment (and the same applied to other phases), whereas the other cables are either cascaded or connected to the undersized extended terminal.  As itsmoked commented, some pictures might be useful.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close