Pump-down cutout setpoint

Pump-down cutout setpoint

Pump-down cutout setpoint

(OP)
Hi,
what is the pump-down cutout setpoint,is it the low pressure cutout,in other hand,can we go lower than that setpoint to be sure that there is no liquid exist on the start-up of the cmpressor,because we have an old trane chiller using the low-pressure cutout setpoint for the pump-down process.

thanks alot.

RE: Pump-down cutout setpoint

old tranes i believe used 25 psig for the pump down , at this pressure there will be no liquid in the evap.and as any liquid boils off the pressure switch will reenergize the compressor and pump the vapor out.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.