clearance requirements for electrical panels per British Standards
What are the clearance requirements for circuit breaker panels - sub main and final distribution - per the British standars?
RE: clearance requirements for electrical panels per British Standards
Marttie:
Refer to BS7671. Most probably you'll have to buy it.
If you mean internal clearances and low voltage - AllenWest panels were built to the following:
BS5486 pt.1 1990
EN60439-1
IEC439-1
Sorry, I don't have copies so I can't tell you any more than that.  The contents page for the IEC spec (costs an arm and a leg) can be found on:
http://webstore.iec.ch/preview/info_iec60439-1{ed4.1}b.pdf
I do have a copy of BS 7671 : 2001.  I have not been able to locate a passage requiring a specific clearance and I've spent considerable time looking.  I'm familiar with the USA National Electrical Code (NFPA 70 - most often called the NEC). It is very specific as the clearances around and above circuit breaker panels for each voltage range.
Thank you to everyone who responded.