Design Conditions for switchgear

Design Conditions for switchgear

Design Conditions for switchgear

(OP)
what is the Indoor Design Conditions for the Switch gear room?

any help/suggestion will be greatly appriciated

RE: Design Conditions for switchgear

most electrical items like to be <85f,<95%rh, i would suggest checking with the manufacturer though,

RE: Design Conditions for switchgear

If you are in the US, the NEC says 90F is maximum without derating conductors.

RE: Design Conditions for switchgear

It depends on if you have transformers that give off heat.  Try to get the electrical engineer to set them outside or hang them on a pole.  If you have VFD's they can also give off heat.  See the manufacturer's data for how much.  If outside air is not too hot then you can ventilate with outside air to cool the space.  Outside air will only get you down to 10 or 15 degrees above outside air temp, depending on how much air you move.

However, some of the electronic devices such as VFD's, TVSS panels or tranfer switches may not be able to handle much heat so you may need to air condition.

RE: Design Conditions for switchgear

A good idea, should you have some extra general exhaust (not toilet or lab hood exhaust, of course)left over as a result of meeting ASHRAE 62 requirements, is to circulate a sufficient quantity of such exhaust through the switchgear room to maintain both humidity and temperature control. The room can be maintained at a negative pressure via a roof mounted or inline fan to allow the easy passage of air from either a plenum source or a ducted system. Maintaining good temp and humidity control in the switchgear room is a good idea for keeping the gear in good condition.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources