relief valve on gas electric heater

relief valve on gas electric heater

relief valve on gas electric heater

(OP)
Does a gas electric heater need a relief valve to protect it in case gas outlet is blocked and heated up?
How can I size it?

RE: relief valve on gas electric heater

I think you need to have safety valve to protect the piping from damage that would lead to significant damage.
Sizing the safety valve depends on the gas properties (expansion coefficient and others) that will be subjected to constant heat flux when the line is blocked.

Hope this would help

Cheers
SmartEngineer

RE: relief valve on gas electric heater

scesare,
I agree with SmartEngineer about the need for a safety valve.  Assuming you can block in the heater and still have it powered up, I think you should size the PSV as follows:
1) Heat enters the system at the capacity of the electric heater; i.e. if the heater's element is 1500 watts, then use 1500 watts as the heat input.
2) You have a confined volume.  Allow the pressure to build to the heater's design pressure.
3) At that point, your safety valve will pop to vent the excessive pressure.  It must be sized to vent gas at a rate rapid enough to avoid any additional pressure buildup.

Note that this is an unsteady state situation.  The quantity of gas in your volume will change with time, as will the flowrate and conditions of the gas you will need to vent.  You might perform calculations at the point where you initiate relief flow and at some time later when a portion of the gas has been discharged.

Perhaps a bigger problem will be one of overheating your equipment.  The heater should always be deenergized when there is no flow.

HTH,
Doug

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources