Is there any rule in the NFPA that will not allow for an Electrical substation with positive pressure ventilation in a Class 1 Div 2 area, within 40 feet from a gas heater?





RE: Electrical Substation and NFPA 497
Assuming NFPA 497 was the Standard used to determine the electrical area classification and NFPA 496 was the Standard used to design/maintain the pressurization of the substation, NFPA 70 (the National Electrical Code) would permit the installation you have described.