Electrical Substation and NFPA 497

Electrical Substation and NFPA 497

(OP)
Is there any rule in the NFPA that will not allow for an Electrical substation with positive pressure ventilation in a Class 1 Div 2 area, within 40 feet from a gas heater?

RE: Electrical Substation and NFPA 497

There are basically three NFPA documents (70, 496, and 497) that collectively address your question.

Assuming NFPA 497 was the Standard used to determine the electrical area classification and NFPA 496 was the Standard used to design/maintain the pressurization of the substation, NFPA 70 (the National Electrical Code) would permit the installation you have described.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources