Fire Dampers
Fire Dampers
(OP)
Trying to locate in NFPA the requirements for testing the fire rated dampers with fuseible links, how often do they need to be tested and when is it required to replace the links.
Thanks
Thanks
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Fire Dampers
At least every 4 years, the following maintenance shall be performed:
(1) Fusible links (where applicable) shall be removed.
(2) All dampers shall be operated to verify that they close fully.
(3) The latch, if provided, shall be checked.
(4) Moving parts shall be lubricated as necessary.