MV System Earthing

MV System Earthing

MV System Earthing

(OP)
Are there examples of either industrial or utility MV (approximately 1 to 33 kV) distribution systems operating without any form of system earth. By any form I exclude even voltage transformer earthing. I mean fully floating.

RE: MV System Earthing

In the first half of the century 440 volt ungrounded delta secondary industrial systems were common. The insulated conductors in conduit formed a capacitor that gave a reference to ground on a system of any size. Not much current. Enough to get a reading on a voltmeter. On a large system enough current to kill you but not enough to burn you. Some old timers would check for voltage by grounding the end of a piece of #14 copper and scratching the other end across the hot terminal. They would get a small spark from the capacitor charging current.
The other connection to ground was the three "Ground detector lights." If you got a ground on one phase one of the lights went out. Usually neon lamps about an inch in diameter were used. I once met an old electrician about a week after he used the old method on a new 1000 KVA 277/480 solidly grounded transformer. His hands were still in bandages the size of boxing gloves.
 
yours

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources