Hello Everyone,

I have a project to install an 18.5MVA Transformer, the client beleives he has an excellent and reliable Differential protection and thus doesnt need an REF protection,how do we convince him.     

RE: Transformer Without REF Protection.

Give the client the pros and cons.  If he chooses not to use the protection you recommend, document it and move on.

Mike

RE: Transformer Without REF Protection.

I agree with mpparent, this is an engineering judgment, not an ethical issue.  There are a lot of transformers that size with just primary fuses for protection.

It's the client's transformer and his money.  

RE: Transformer Without REF Protection.

Hello a430
If the transformer is solidly grounded then I do not see any significant advantage of providing REF protection on top of differentioal protection.

RE: Transformer Without REF Protection.

I think that earth-tank protection can replace the REF and is much easier to implement, however it needs the transfomer to be insulated from earth;

RE: Transformer Without REF Protection.

It all depends on the transformer winding configuration, the grounding arrangements, the importance of the transformer, how quickly it can be replaced or repaired if an internal fault occurs, and the degree of protection you want to apply. A 18.5MVA transformer is not an of-the-shelf item - in my opinion the more reliable protective schemes, the beter. Depending on the winding configuration, an additional REF-scheme incorporated into the diff-scheme (to obtain a combined REF/diff scheme) can easily be implemented, and it needs just a few extra items.

Finaly, as pointed out by several posters, the final decision depends on the client. Show him the advantages and disadvantages and let him makes the desicion.

Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon

Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources