pH of run-off water
pH of run-off water
I may be in the wrong forum, thought I'd start here. We have a few spray pads in our parks. All but a couple are concrete structures. These others have asphalt for the pads. The pads are like a cooling fountain for kids to run around in. The water runs into the drains, into a tank, pumped through filters, treated then pumped out again. (Conservation). The pH is easy to maintain on the concrete pads, however the asphalt pads are very difficult to maintain neutrality, it climbs dramatically, well above 8.5. Should asphalt have this affect?
RE: pH of run-off water
Not sure what time frame that you are talking about in regards to your samples. But what happens in a cooling tower for instance, is that the water evaporates and causes the alkalinity to increase with a corresponding rise in water pH. What is commonly done in cooling towers is to feed acid to lower the pH.
If you are feeding well water containing carbon dioxide, you may also be getting an effect where the pH increases as the carbon dioxide is being stripped into the air.
You may want to increase your blowdown and increase your water makeup to counter the effects of evaporation.
If you have a complete description of your system and water analyses, it would be helpful for further diagnosis.
Thanks for your reply. These pads are essentially large, group showers. On a hot sunny day the kids in the park run up to it, push a button and the water flows out a "shower head" in a 10 or 15' diameter for a timed period. The water is contained on the pad, drains through a filter into an underground water tank (5000 gal) and is treated before it gets pumped back up to the shower head. The concrete pads require very little treatment to maintain pH 7.2 or so. The asphalt pads rise in pH to 8.5 in one day. Because of evaporation, our city water keeps the levels up in the tank. Our city water is soft and about 6.4 pH. With the makeup being higher in the asphalt pad (more evaporation) we would expect lower pH. Not the case. It has been suggested the oil in the asphalt is causing this.
Any thoughts?
You probably get more evaporation from the asphalt units because the dark material absorbs more of the sun's heat than the lighter color of the concrete.
With a higher evaporation rate, the alkalinity will increase more in the asphalt units than the concrete units, driving the pH up. You also have some carbon dioxide in your water as evidenced by the low pH. The carbon dioxide will also air strip, driving the pH up.
Why don't you check the temperature in the ponds and see if each pond is the same temperature. Also, see if you can measure the water input to each pond.