×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

Open Bypass for Thermal Relief

Open Bypass for Thermal Relief

Open Bypass for Thermal Relief

(OP)
Right now we have a styrene line that has about 400 foot of piping that is 4" Sch. 40.  It pumps styrene into a reactor at around 2000 lb/min.  There is a blocked in section that is blocked in by 2 valves.  In the past, they installed a bypass that went around one of the valves and instaleed a valve in it.  The bypass is about 9 feet long and reenters into the main header behind the first block valve that blocks in the section.  The valve in the bypass is closed when pumping and open when not.  Problem is the valve in the bypass gets plugged up a lot.

Is there a good reason not to just remove the bypass valve except loss of flow rate while pumping to the reactor?  What would be the best way to calculate the loss of flow while having the bypass open?

Thanks.  A 1989 article in CHE Mag. is where I got this idea.   

RE: Open Bypass for Thermal Relief

Are you thinking of replacing the bypass valve with a PRV?

RE: Open Bypass for Thermal Relief

(OP)
No not a PSV.  Just an open bypass that will relieve the fluid whenever the blocked in section valves are closed.

RE: Open Bypass for Thermal Relief

If you remove the bypass valve, how are you planning to relieve the fluid between the 2 block valves?

RE: Open Bypass for Thermal Relief

(OP)
When the valves in the main header is closed, the open bypass might also be full but where it bypasses to (from in between the 2 valves to before the first valve)is not blocked in.  This will relieve the fluid blocked in.

Thanks.

RE: Open Bypass for Thermal Relief

If the bypass valve line runs parallel to the main line downstream of the pump.  Which is what I think you are saying, then you won't loose any flow when the pump is running.

If the bypass outlet is in front of the pump and the bypass inlet is down stream of the pump then the pumping loss will be the amount of material that can flow through the bypass line at a differential pressure equal to the operating pressures.

You might want to put an orfice plate in the line to slow it down a little but it sounds like a good solution to the problem.

Regards
StoneCold

RE: Open Bypass for Thermal Relief

(OP)
Thanks for the info.  The bypass inlet and outlet is both on the discharge side of the pump.  The bypass is pretty much a loop around with 2 elbows going around the block valve.  So no losses in pumping capacity should occur.  

Thanks.

RE: Open Bypass for Thermal Relief

RJB32482,

Just to point out the obvious, one reason for not removing the bypass line's block valve is you may not be able to easily isolate the line that you are trying to protect.  Are there times when you may need to have the line completely isolated and how do you plan on accomplishing complete isolation if there is a bypass line without a block valve.

Also, do you know why the bypass line gets plugged up?  I don't have experience with styrene but isn't it prone to polymerization even at room temperature?  I can imagine a dead leg of stryene could be a problem over time but in a small diameter line that essentially has no flow through it, I can imagine even without a block valve, the bypass line may still have a plugging problem.

You may want to go back to the root cause of your concern, why is it necessary to block in your 4" line in the first place?  Are there other means of avoiding overpressure of the 4" line from thermal expansion of the liquid?  If you presently have a procedure that says open the bypass valve when you block in the 4" line, why not just make your procedure be that you never close one of the valves in the 4" line?

RE: Open Bypass for Thermal Relief

(OP)
One of the valves in the 4" line is for the whole styrene header system and the other valves are for each of the reactors.  So you can't just open the 4" valve in the main header line.  

Thanks

RE: Open Bypass for Thermal Relief

EGT01 Makes a good point.  Even if you decide to leave the bypass open most of the time, you should at lease have a block valve there.

Regards
StoneCold

RE: Open Bypass for Thermal Relief

(OP)
Increasing the line to 2" might help in the plugging factor while still not effecting the flow rate.  Any thoughts if this would help or not?

Thanks.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources