HV Substation Bus Dampening Conductors

HV Substation Bus Dampening Conductors

HV Substation Bus Dampening Conductors

(OP)
Well here we go!  I hope that this discussion will spark some interest and benefitial information exchange.  I am in the process of writing a new standard for our company.  The new standard deals with dampening cable inside horizontal Al. bus in electric substations.

First off here is a list of the current sizes that we have as min. diameter.
       bus size         min size of acsr
       2                266.8
       2.5              266.8
       3                266.8
       3.5              397.5
       4                795
       5                1431
       6                1590


There are several questions that come up.  Your professional opinions and career experiences will be of great help.

First,  Do we have to use ACSR? Or will AAC work?
        What about the newer conductors available ACCC?

Second, Are the above min. sizes ok?  and what is the max.
        size?

Third,  Is the dampening characteristic of the conductor
        within the bus a function of the size ie the cross
        sectional area, or weight of the conductor or both?

Fourth, How long is the max bus length that does not
        require dampening?

Thank you for all your input and help.
 

RE: HV Substation Bus Dampening Conductors

I believe that some of your answers can be found in ANSI/IEEE Std 605-1987, IEEE guide for design of substation rigid-bus structures.  If you are writing standards for your company about rigid bus, you need to have a copy of this standard in any case.   

RE: HV Substation Bus Dampening Conductors

First,  Do we have to use ACSR? Or will AAC work?
        What about the newer conductors available ACCC?

I don't think I would use ACSR. We use AAC

Second, Are the above min. sizes ok?  and what is the max.
        size?

Those sizes seem very large.

Third,  Is the dampening characteristic of the conductor
        within the bus a function of the size ie the cross
        sectional area, or weight of the conductor or both?

Since it is INSIDE the bus, it has to do with weight and the damping effect. A lot of times the smaller wire will jump inside the bus helping damp the bus. Heavy ACSR that doesn't move may amplify the bus shake.

Fourth, How long is the max bus length that does not
        require dampening?

We use it with any span over 10'.

JTK

RE: HV Substation Bus Dampening Conductors

1- Do we have to use ACSR, AAC or ACCC?  To reduce bus vibration, any material will help to reduce the vibration. However, dissimilar materialhelps. However, to avoid galvanic corrosion disimiles materials should not be used.

2- Are the above min. sizes ok?  What is the maximum size? Economics ussually is the limiting factor for the miximum size. In general, the  IEEE Std 605 suggests a range as follow:  
                                             10% < conductor/bus weight < 33%.
NOTE: The standard also recognizes that less cable may be sufficient in some cases to reduce the vibration to acceptable levels.

3- Is the dampening characteristic of the conductor within the bus a function of the size i.e. the cross sectional area, or weight of the conductor or both? The natural frequency of the bus & cable combined is direct proportional to the moment of inertia of the cross sectional area and inversely proportional to the mass per unit length. There are other factors such as bus span length and type of support (fixed or pinned end).

4- How long is the max bus length that does not require dampening? Two criteria are suggested by the standard to determine the maximum length base in the bus natural frequency, system and aeolian frequencies as follow:

1)   fnatural> fsystem ==> Bus span should be changed or detail dynamic analysis is required to determine level of stresses.

2)   fnatural>  faeolian/2 ==> Bus span should be changed or dampening is required.

RE: HV Substation Bus Dampening Conductors

(OP)
Doesn't the standard call for dampening is the natural freq is less than twice the aeolian freq?

RE: HV Substation Bus Dampening Conductors

Is the same as note above in answer 4.2:

         fnatural>  faeolian/2    or
         2fnatural>  faeolian
==> Bus span should be changed or dampening is required.

RE: HV Substation Bus Dampening Conductors

Quote:

standard call for dampening is the natural freq is less than twice the aeolian freq
is not the same as

Quote:

fnatural> faeolian/2==> Bus span should be changed or dampening is required.
but the latter is correct.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources