Horizontal tanks used Vertically

Horizontal tanks used Vertically

Horizontal tanks used Vertically

(OP)
MY question is in regards to the use of a horizontal petroleum storage tank (20,000 gallon) in a vertical position.  I have a customer that has done this without notifying anyone.  What should my concerns be regarding the safety of this practice.  The tanks are most likely 1/4 inch steel walls with 3/8 heads.  The tanks are approx 30' long and 10' in diameter.  Is this a safe thing to do?  Obviously if I get the specific specs on the tanks I can calculate shell stress and thickness adequacy based on API 650, but has anyone actaully ever seen this happen?  Thanks all.

Chris

RE: Horizontal tanks used Vertically

I think if you look at UL-142, you may see that the tank wall thickness may be the same.  If it's a flat head, I don't see much in the way of a potential problem.  Stresswise, a UL-142 tank in a vertical position has much lower shell stresses that a horizontal tank sitting on saddles.  What could be of great concern would be the vents and manholes.

Steve Braune
Tank Industry Consultants
www.tankindustry.com

RE: Horizontal tanks used Vertically

(OP)
Steve,

Thanks.  That is exactly what I needed to hear.

Chris

RE: Horizontal tanks used Vertically

Chris,
Please be sure to check out UL142 yourself.  Don't rely upon the musings of us folk without all the info.

Steve Braune
Tank Industry Consultants
www.tankindustry.com

RE: Horizontal tanks used Vertically

Check for wind overturning when empty- they probably won't check out for that.

RE: Horizontal tanks used Vertically

(OP)
I certainly will.... thanks for the help.

C

RE: Horizontal tanks used Vertically

TECHNICAL NOTE: Unachored and Anchored Liquid Storage Tanks

Is the tank unachored or anchored.
checking for sloshing and overturning

If anchord check for base share.

If unachored use advance search for the free computer program for unanchored tank.

Additional requirement thread794-139620

RE: Horizontal tanks used Vertically

Vessel design is not expertise so I would like to hear comments from the others but whether it is UL-142 or API 650, I believe both of those are atmospheric storage tanks meaning they would have been designed for a low MAWP rating (at top of vessel) plus liquid static head.  I would have some concern for how much liquid level would be allowed in the vertical orientation since in that position you would have 3x the static head the vessel would have been designed for and that would seem to be a significant factor.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources