Transformer cooler design
Transformer cooler design
(OP)
I am looking at changing a xfmr from ODWF to OFAF/OFAN. If i change the heat exchangers, do I need to worry about the pressure from the pumps?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Transformer cooler design
|
RE: Transformer cooler design
Whe u say -"If i change the heat exchangers", are u incorporating radiators etc. If not i dont know why u should worry about the pressure. Pressure was critical only when water was on the other side. But your transformer was always under the pump pressure, isint it?
RE: Transformer cooler design
The pumps may not be able to deliver the same cooling flow through the xfmr if the pressure loss across the new heat exchanger is greater.
Here are some basic questions that should point you down the right path.
Does the xfmr use a centrifugal pump?
What is the rated cooling flow and pressure loss across the old and new heat exchangers?
What is the rated pump pressure and flow (at what fluid SG)?
Is there a significant diffence in the specific gravity of ODWF and OFAF/OFAN?
Will the new heat exchanger change the average fluid operating temperature?
RE: Transformer cooler design
Not quite sure where that was going:
ODWF = Oil Directed, Water Forced
OFAF = Oil Forced, Air Forced
OFAN = Oil Forced, Air Natural
Questions:
Why are you changing the OD** designation to OF**? There seems little point in interfering with the internal oil flow for the transformer. The oil directors are usually intended to provided additional cooling at likely hotspots within the design. Are you implying that you are going to remove them?
Using OFAN is a relatively unusual mode - ONAF is the more common intermediate step prior to OFAF as it accumulates wear on the easy-to-maintain external fans and minimises running hours on the pump. Fan maintenance on an ONAF design typically doesn't require the transformer to be out of service unlike pump maintenance on an OFAN design (unless you have redundant pumps and isolation valves for each pump - a rare luxury except on very large or system-critical transformers!)
You will almost certainly have a lower pressure drop across a finned air radiator bank than an oil/water heat exchanger. You should check that the pump is suitable for service at a lower pressure, higher flow situation. Changing the pump performance may have knock-on effects on the efficacy of the oil directors at cooling the hot areas of the transformer. You should study the oil flow path very carefully and try to ensure that the conditions do not change significantly from the original design.
The best people to discuss this with are the transformer's manufacturer. What have they said about this proposal?
----------------------------------
I don't suffer from insanity. I enjoy it...
RE: Transformer cooler design
I want to remove water coolers & put radiators on... (for reasons that arent very relevant here so I wont go into them). so there are currently pumps on there.
I'm trying to decide whether I wanna leave those pumps on or not, and whether or not they will destroy the radiators.
I'm thinking of running the pumps @ lower power...
RE: Transformer cooler design
RE: Transformer cooler design
As a transformer manufacturer engineer I can call your attention to two points: first, that a pump to work in an ONAN mode must be radial type (centrifugal are often used with pure ODAF heat exchangers!) to have low pressure drop when stopped, and second, you must have a head-vs-flow working point that insures an oil speed that while being enough for the expected cooling will not generate static charges in the insulating material. This speed must be indicated by the manufacturer; only him has elements to calculate the internal pressure drop and the optimal oil speed (I use to limit to about 12 to 13 cm/s in txfs >100 mVA, >230 kV).