Modeling a VFD in SKM

Modeling a VFD in SKM

Modeling a VFD in SKM

(OP)
I have been using SKM for quite a few years for short circuit analysis and load flow calculations. I have always modeled VFD drives and DC drives as a Non-Motor Load. Is this the best and most accurate way to model these devices?

RE: Modeling a VFD in SKM

If the concern is the short-circuit contribution, then you should model as non-motor load, since the typical VFD will not contribute to fault current.  The only exception would be regenerative or four-quadrant type drives.  These can supply current to an upstream fault, but at a lower value than a motor running across-the-line.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources