fiber optic cable installation .
The fiber optic cables transmit light rather than electronic signals eliminating the problem of electrical interference . Then why as per NEC 770.52 the conductive optical fiber cables are not permitted to occupy the same cable tray or race way with conductors for electric light ,power .
Also It is understood in electrical industry that a metal-clad (MC) gets the same treatment as conduit with regards to cable separation .MC cable is a manufactured assembly of flexible conduit and cable and flexible conduit by NEC definition is a raceway (art 100)
So can the power, type MC cable , be laid along with fiber optic cable non conductive and conductive type ?? in the same cable tray .
RE: fiber optic cable installation .
"Nonconductive optical fiber cables, but not conductive optical fiber cables, can occupy the same cable tray or raceway as conductors for electric light, power and Class 1 circuits operating at 600V or less (see Figure 770-10 un770-10 770-52A 02.cdr)."
This is in the "MIXING FIBER and ELECTRICAL" section of:
http
I understand that to prevent the accidental energization of the conductive material in fiber optic it is essential to separate the conductive fiber optic from class 1 and power cables , but still cannot interpret the nec code properly ,whats the thinking behind separation .