ramblings of a construction inspector
We have 1’-6” foundation walls with verticals of # 9 @ 12” OF and # 8 @ 12” IF and horizontals of # 5 @ 12” EF. The contract drawings have a wall section detail (side view) that clearly shows the horizontal bars inside the vertical bars on both IF and OF mats. The foundation walls are different from the shearwalls which have the horizontals bars outside of the vertical bars on both IF and OF mats. However, the plan view detail depicting the typical wall corners, ends, and intersections only shows horizontal bars outside of the vertical bars on both IF and OF mats. All wall corners, ends, and intersections require “U” bands lapped with the horizontal bars.
Of course the rebar bender made the U bands to fit outside of the verticals as the typ detail shows. U bands are only shown in the typ detail (plan view) not in the wall section detail (side view).
At the beginning of rebar placement for a large section of foundation wall I informed the contractor (prime) of this discrepancy: that the U bands were fabricated to fit on the outside of verts rather than the inside of verts where the horizontal bars were. An RFI was sent up and an answer was sent back down. The contactor (rebar sub) told me that the engineer wrote that it was OK for the U bands to be on the outside. Three days later (1 day rebar + 2 days formwork) after the rebar was installed and 90% of the formwork was in place and with concrete scheduled just hours away I just happened to eyeball the RFI on the contractor’s desk and the answer read the exact opposite of what the rebar sub said it read. The engineer clearly wrote that on shearwalls the U bands were to be on the outside of verts and on foundation walls the U bands were to be on the inside of verts. I instantly picked up the phone and called the guy and said hey they have it reversed from your answer on the RFI. He said I was reading right that the U bands were to be on the inside of verts for fdn walls. I brought this to the attention of the contractor and that I would have to report this discrepancy in the inspection report.
With the prospect of having to change 3 days worth of work to get those U bands right, the contractor got the boss of the engineer to change the RFI to now read that all U bands could be placed on the outside of verts regardless of where the other horizontal bars were.
Did the rebar sub pull my chain and tell me a fib or were the instructions which went from prime to formwork sub to rebar sub lost in translation? We may never know for sure but my old SOP of “If it isn’t in writing it doesn’t exist.” has been firmly reinstated. Seeing is believing, right?
Also, what's the big deal on these U bands if they are inside or outside and lapping or not lapping with the horizontal bars? They are just for containment, right?
RE: ramblings of a construction inspector
The situation you pointed out is fairly typical - shearwalls have horizontal rebar on the outside and foundation walls etc. have it on the inside. This is primarily because foundation walls are resisting bending and you get a large effective section depth if your main vertical rebar is closer to the ouside of the walls (thus placing your horizontal rebar on the inside of the vertical rebar).
For shearwalls which are resisting in-plane forces it doesn't matter as much and therefore the extra confinement of the vertical bars provided by the horizontals on the outside as well as the easier constructibility of horizontals on the outside typically lead to that arrangement.
Richard A. Cornelius, P.E.
WWW.amlinereast.com