Hi, I'm hoping someone here can clarify NFPA 54 requirement for outdoor combustion air for me.

Section 8.3.3 calls for openings in boiler room enclosure of 1 sq.in./2000,3000,4000 Btu/hr of input depending on method. The openings shall communicate directly, or by ducts, with the outdoors or spaces that freely communicate with the outdoors.

While opening sizes in the boiler room is quite clear, what's not clear is the area required for the connecting duct and louver. Someone said to size them at 12 CFM/HP at .005" pressure drop, someone else emailed me a chart of manufacturer's recommendations, another said to use same area as required openings in the boiler room.

Need a little guidance here on code compliance. Thanks.

RE: Combustion air opening

same area as required openings in the boiler room.

RE: Combustion air opening

MagicJS,


Here in Tennessee, code officials interpert that to say that the free area of the duct and the free area of the louver are to conform to the SqIn/BTU rule.  

ie.  A 1000MBH boiler requiring 1 sqin/4000 btu will need 250 sqin area duct.  If you use a std louver with ~ 75% free area the louver will need to be ~ 333 sq in.

For large boilers, (Where there is not enough wall to satisfy the natural ventilation or where freeze protection is important) I engineer a combustion fan sized to provide the CFM of air required for combustion and interlock fan with boiler safties.  This sometimes takes a little explaining to the boiler official.  

Earl M Keith, PE
Tennessee

RE: Combustion air opening

that 12 cfm / bhp is based upon excess air combustion calculations

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources