(OP)
I have a small facility fed from three 2.5 Mva 480/480-277 transformers. The secondary feeds gear housing three 1500 amp Pringle fused switches, each of which are protecting a load. which are 1:Process machinery, 2:facilities equipment, and 3: a lighting Panel board.

When a ground fault occurs on a small motor everything in the whole operation shut down. . We are considering installing a High Resistance Grounding system where we would lift the primary "center tap" ground connection to the grid and route the secondary "center tap" connection thru the HRG circuit then back to ground.

We are also considering putting a transformer between the gear and the Panelboard to isolate the single phase loads.

Does this sound like a reasonable solution to our Ground Fault dilema?

RE: Wye/Wye Distribution problems.

If you have any 277V loads you cannot use an HRG system.  Far and away the easiest solution would be a second level of ground fault trips and a coordination study to determine where to set each trip.  I don't know how you define small motor, but if every thing is set properly, ground faults on small circuits, say 30A and less, should be able to be cleared by the branch breaker before the ground fault trip at the Pringle switch picks up and trips, but not if the ground fault is still at its minimum pickup, fastest trip as it came from the factory.

RE: Wye/Wye Distribution problems.

Why do you state that if you have any 277V loads you cannot use an HRG system? Under what conditions is an HRG system allowed?

RE: Wye/Wye Distribution problems.

NEC 250.36

RE: Wye/Wye Distribution problems.

It's allowed when there are no 277V loads, basically for 3-wire systems with no active neutral.

RE: Wye/Wye Distribution problems.

(OP)
Our intention was to route the feeder to the single phase distribution panelboard through a delts/wye transformer and develope a neutral specifically for these loads.

The gear is 2o+ years old and the Pringle switches are LBFs.  

RE: Wye/Wye Distribution problems.

Are the ground fault trips on the Pringle switches set where the coordination study says they should be set?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources