19 strand tendons

19 strand tendons

19 strand tendons

(OP)
We have a group of 12 tendons, each tendon consists of 19 strands (15.7mm diam 7 wire strands). For various specialist prestressing companies such as VSL Dywidag, Freyssinet what is their recommended minimum radius of curvature if the tendon is to be post tensioned within a corrugated steel duct.

For BS, PTI, DIN etc what are their recommended minimum radius of curvature.

Can anyone provide some assistance, perhaps a couple of Engineers can each provide some data so that I can draw up a comparison table.

Any more info needed? any help gratefully received

RE: 19 strand tendons

Zambo,

VSL - approx 6500mm
BBR - 6000mm

RAPT - 6650 (based on 70 * duct ID)

I cannot find Freyssinet's at present but it is in the order of 6500mm as well

RE: 19 strand tendons

(OP)
rapt,

thanks for the quick response. Duct internal diameter is 95mm. I have found Freyssinet and it is 100x i.e 9.5m. Does this info change the VSL or BBR?

What is RAPT?

for PTI I have 21feet curvature around an obstacal = 6.6m

thanks

RE: 19 strand tendons

Zambo,

No, the VSL and BBR figures are from their brochures. I did not think that the Freyssinet figures were usually that much higher.

RAPT is a computer program I develop and market around the world.

These radii are the absolute minimum values you would normally use over supports etc to ensure the compression on the inside of the curve will not crush the concrete or cause a butsting problem. If you are going to use them for horizontal curves, I would use much higher figures or look at the stresses induced in the concrete from the curves if you use the minimums.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources