What is the recommended voltage test level on a transformer winding. My old rule of thumb is 2x the working voltage. Is this OK with a DC tester?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Transformer Hi-Pot testing
|
RE: Transformer Hi-Pot testing
Disconnect all high, low and neutral connections. Tie all high voltage connections together, all low voltage connections together with neutral. Megger, and maintain for 1 minute,
1) the high voltage winding to low voltage(with Neutral)and to ground,
2) High voltage winding to ground,
3) Low voltage winding to high voltage winding and to ground,
4) Low voltage winding to ground,
5) and High voltage winding to low voltage winding.
For oil filled transformer:
Transformer Voltage: 0 -600, DC test: 1000V, Min acceptable resistance: 100 Mohms
Transformer Voltage: 601 - 2500, DC test: 2500, Min acceptable resistance: 1000 Mohms
Transformer Voltage: 2501 - 15000, DC test: 5000. Min acceptable resistance: 5000 Mohms
I don't know if these are the recommended test voltages or where the source came from. Unfortunately, that is not documented in our test procedures.