Steam Piping
Steam Piping
(OP)
I need to supply steam to a heater and an eductor in a small enclosure (20"x20"x8") that is attached to a vessel nozzle. The steam flow through the eductor will be the motive fluid to create a suction to get our sample from a flue gas stack.
The vendor indicated they'll need between 20-80 psig steam for the eductor. I located a nearby 3/4" 150# steam pipe that ultimately drops down to steam tracing. I intend to tap into this line and run piping about 6' vertically to a deck where I will put a steam reduction station. The 3/4" pipe will be split into two 3/4" branches with each going to a Fisher 95H steam regulator. The steam will be adjusted to the needed pressure then exit each regulator via preinsulated stainless steel tubing. The tubing will travel vertically about 35 feet to the enclosure.
Questions:
1. The operator indicated the line I want to tap into is a 150# steam line. I did find iso's and drawings to agree with this. Which pressure and temperature do I use for calculations since there are no gauges or indicators? Do I assume saturated steam to be conservative or superheated? If I assume saturated, then any heat loss will generate condensate immediately. I do have some data from the plant stating that when designing for the 150# steam system, use the following for utility characterisics:
Process 410 deg F and 150 psig
Mechanical 450 deg F and 170 psig
Considering the tap off the main header could be a long distance from my work area, I'm concerned that I may be using inaccurate data.
2. Where should I install steam traps in this piping? I intended to put one in the common piping upstream of the two regulators. Is this an appropriate location considering I'd have a reverse flow situation. I assume there will be condensate formation at the upstream side of the regulator (is this correct?) If so, that condensate wouldl be flowing against the steam flow to the regulator.
3. Do I need another steam trap before I make the 35' climb in pre-insulated SS tubing?
4. Do you think a 3/4" 150# steam line would be sufficient to supply a constant 20-80 psig stream to the eductor and a branch for a temperature regulated enclosure heater?
I am a new mechanical engineer and work with a firm that is primarily an electrical company, so I have no experienced people to turn to. This adds a bit of complexity to my work, but having you guys is an asset.
Thanks for your time.
The vendor indicated they'll need between 20-80 psig steam for the eductor. I located a nearby 3/4" 150# steam pipe that ultimately drops down to steam tracing. I intend to tap into this line and run piping about 6' vertically to a deck where I will put a steam reduction station. The 3/4" pipe will be split into two 3/4" branches with each going to a Fisher 95H steam regulator. The steam will be adjusted to the needed pressure then exit each regulator via preinsulated stainless steel tubing. The tubing will travel vertically about 35 feet to the enclosure.
Questions:
1. The operator indicated the line I want to tap into is a 150# steam line. I did find iso's and drawings to agree with this. Which pressure and temperature do I use for calculations since there are no gauges or indicators? Do I assume saturated steam to be conservative or superheated? If I assume saturated, then any heat loss will generate condensate immediately. I do have some data from the plant stating that when designing for the 150# steam system, use the following for utility characterisics:
Process 410 deg F and 150 psig
Mechanical 450 deg F and 170 psig
Considering the tap off the main header could be a long distance from my work area, I'm concerned that I may be using inaccurate data.
2. Where should I install steam traps in this piping? I intended to put one in the common piping upstream of the two regulators. Is this an appropriate location considering I'd have a reverse flow situation. I assume there will be condensate formation at the upstream side of the regulator (is this correct?) If so, that condensate wouldl be flowing against the steam flow to the regulator.
3. Do I need another steam trap before I make the 35' climb in pre-insulated SS tubing?
4. Do you think a 3/4" 150# steam line would be sufficient to supply a constant 20-80 psig stream to the eductor and a branch for a temperature regulated enclosure heater?
I am a new mechanical engineer and work with a firm that is primarily an electrical company, so I have no experienced people to turn to. This adds a bit of complexity to my work, but having you guys is an asset.
Thanks for your time.





RE: Steam Piping
http://www
KRB
RE: Steam Piping
Don't assume anything. Find a way to trace this line back to its source or get some instrumentation (a IR temperature gun for example) and find out what your steam conditions are.
It is critical to your jet operation that the steam conditions be what the jet is designed for within tight tolerances.
Put a moisture separator before the steam jet.
You didn't say whether your vertical runs were upwards, or down, or at least I couldn't understand it.
That ought to give you a couple of places to start with.
rmw
RE: Steam Piping
Design conditions: Pressure - where the lowest relief valve settings is set. Temperature - the max temperature expect with the desuperheaters are failed.
Operating conditions: Where you hope to control the temperature and pressure with desuperheaters and reducing valves.
You design the pipe for operating conditions, but make considerations for saturated conditions for trapping the pipe.
My rule of thumb for trapping - trap a line when it rises or else hammering will occur AND trap a line at a location before a control valve or shut off valve to prevent condensate build up and corresponding big condensate slug on start up.
My other suggestion - the cost difference between 3/4" pipe and 1" pipe is nothing - but you didn't mention steam flow to verify pipe sizing. You will have steam flow to an eductor to influence flow. An eductor completely uses all the steam used to circulate the fluid. There should be an amount of steam that will be used. Use this to size your pipe.
This is a great site for sizing steam pipe - just for a quick off the cuff calculation:
http
RE: Steam Piping
write the job requirement spec, and give it to a piping company.
RE: Steam Piping
Everybody has to learn sometime. A combination of reviewing the Spirax manual and having an experienced piper install is something that can help someone learn.
I'll say it again.... everybody has to learn sometime.
If it's a socket welded system and proper NDE is performed and the system is trapped right.
RE: Steam Piping
KRB