ASME I vs. VIII Safety Reliefs
What is the difference between a Safety Relief Valve manufactured to ASME I vs. ASME VIII as far as deign and function? This would be for steam service at pressure below 250 psi.
RE: ASME I vs. VIII Safety Reliefs
Variations between sect I and VIII include the types of relief devices allowed, the max allowable overpressure, and setpoints.
Section VIII valves are for unfired pressure vessels. The spring is usually enclosed, but open springs and/or alloy are optional. Rated capacity is at 10% overpressure,16% permissible with multiple valves and 21% permissible for Fire rating. Blowdown is customarily also 10% but I was told recently that the code does not stipulate this and I have not checked to verify. There is only one adjustment ring. A lifting lever is only mandated for air, steam, or water over 140F. Section VIII valves are available with optional bellows-balanced discs so they can be piped to a recovery system with variable backpressure. Section VIII valves are also available with pilots instead of spring-loading, where the process pressure is used to hold the valve closed until the pilot trips. Pilot valves are much more compact and seal tighter as the pressure increases---usually have soft seats. But with the small flow passages to and in the pilot they are not tolerant of contaminants in the process
J. Alton Cox
www.delucatest.com