CRACK CONTROL IN FOOTINGS
I am working on the design of a footing that has two way flexure. Do I have to check the footing for crack control?
Rob
Rob
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
CRACK CONTROL IN FOOTINGSCRACK CONTROL IN FOOTINGS(OP)
Thanks, Rob Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
RE: CRACK CONTROL IN FOOTINGS
Why would the footing crack? If shrinkage, how big is the footing?
What other reinforcing steel is in it (if any)
Crack control is not required for the base of concrete footings. I have even seen this requirement waived for concrete with at least 500mm of earth cover.
VOD
A "fringe benefit" for "typical" sized footings (like you are describing) is that cracking because of flexure is normally not a problem. Wise to check, however.
www.SlideRuleEra.net
Rob
Why would you have different reinforcement in each direction in a square 2 way flexural footing? It should be reinforced like a 2way slab! And as it is symmetrical, so should the reinforceemnt be.
Or am I mis-understanding where you are putting the shrinkage reinforcement.
You have not said what the exposure is. If the soil contains anything corrosive, then yes, I would be checking for crack control. In fact, I would probably do it anyway as it could possible be permanently wet.
houseguy,
It is a flexural footing. They crack because they are flexural reinforced concrete and bending and shear stresses are induced in them from the pressure from the soil.
The reinforcement is same in both directions. I missed a word "top" in my previous reply, #5 @ 12 is at the top for shrinkage.
