Cladding and Components wind load combination
(OP)
How are wind cladding loads combined? For example a corner of a building, how are the wind cladding loads combined, for design the corner support?
To the best of my knowledge the ASCE 7 code does not address cladding load combination, it applies orthoginal loads seperately. I see the corner having a pressure applied on one side and a suction on the other.
I believe it to be overly conservevative to apply full pressure to one side and full suction to the other.
Are the Main Wind Force Resisting System load combination applicable to cladding? (They specify 3/4 load in each direction)
Thanks
To the best of my knowledge the ASCE 7 code does not address cladding load combination, it applies orthoginal loads seperately. I see the corner having a pressure applied on one side and a suction on the other.
I believe it to be overly conservevative to apply full pressure to one side and full suction to the other.
Are the Main Wind Force Resisting System load combination applicable to cladding? (They specify 3/4 load in each direction)
Thanks





RE: Cladding and Components wind load combination
ASCE 7 provides applicable component/cladding wind loads at specific locations on a structure. There is no combination with other wind loads (such as MWFRS loads). Just wanting to better understand your question.
RE: Cladding and Components wind load combination
The situation I am questioning is a cladding anchor that has cladding attached to it in both the x and y directions. I believe full pressure in the x direction and full suction pressure in the y direction is overly convervative, but I have not found any direction as of yet.
Hopefully this helps.