Our architect has provided me a wood truss, wood stud Church.  There are are dormers with windows that start below truss bearing, continuing above truss bearing, cutting the traditional double top plate collector/chord (depending on the load direction) that typically runs the length of the building.  The condition exists on both sides of the building, cutting the collector/chord on the long length of the building (parallel to the ridge of the building.)
For longitudinal wind, I have a short diaphragm to shear walls on either end of the building.  For transverse wind, I'm thinking that there needs to be drag struts at the location of the cut chords, forming smaller diaphragms between the larger diaphragms.  These drag struts would not rest on shear walls, but server to transfer the load from the larger diaphragm to the smaller one back to the larger one.  I have no idea on how to compute deflections of this irregular diaphragm.  Am I on the right track here?  Did I mention scissor trusses and a 12:12 roof pitch?

RE: Window/Dormer Cuts Wall Collector

You have mentioned one possible solution.

Another possibility--can you treat the diaphragm for transverse lateral loads as two separate three sided diaphragms (each open on the side at the dormer)?

DaveAtkins

RE: Window/Dormer Cuts Wall Collector

(OP)
The condition occurs 3 times in the roof, so I would have a couple of isolated diaphragms with the 3 sided diaphragms.  I don't think that that option will work.  Always open to suggestions though.

RE: Window/Dormer Cuts Wall Collector

Tricky problem.  Somehow you need to get those chord forces around the dormers.  If the chord force is small, perhaps some of the roof sheathing can do the job (I believe this is not a "kosher" way of taking chord forces, but I have done it for small forces).  Or perhaps use blocking between the trusses, and use Simpson straps to tie the pieces of blocking together.

DaveAtkins

RE: Window/Dormer Cuts Wall Collector

(OP)
Are you saying that, at the thinnest part of the whole roof, use that as a diaphragm width, creating the chords the full length of the building using the strapped blocking parallel to the ridge.  I think that could work.  It would be uniform and deflections would be simple.

RE: Window/Dormer Cuts Wall Collector

Yes.  And you would not necessarily need to run the strapping the whole length of the building, if at the ends of the building the wall top plate can start taking the chord force.

DaveAtkins

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources