Energising a 500kVA Tf from a 830 kVA Generator
4

Energising a 500kVA Tf from a 830 kVA Generator

Energising a 500kVA Tf from a 830 kVA Generator

(OP)
Will the inrush current to the generator circuit breaker be less if there is a small load on the 500kVA transformer?

RE: Energising a 500kVA Tf from a 830 kVA Generator

Inrush won't be less in magnitude, but will be damped out faster if the transformer is loaded.

RE: Energising a 500kVA Tf from a 830 kVA Generator

Eri62,

Can you directly the transformer to the generator and avoid inrush by allowing the generator's AVR to bring the voltage up gently? If you switch on the other (HV? LV?) side of the transformer then you avoid inrush due to the transformer and make life easier for your generator. If you do this you should consider extending the generator's zone protection out to cover the transformer too.

----------------------------------
  I don't suffer from insanity. I enjoy it...

RE: Energising a 500kVA Tf from a 830 kVA Generator

If i were u i would do exactly like Scotty UK suggested. Why not ramp up the voltage slowly when u can.

RE: Energising a 500kVA Tf from a 830 kVA Generator

Damping of transformer inrush oscillations can be done with either a load connected to the transformer secondary or the primary. The idea is for energy that returns from the transformer during the inrush period has a place to go. There will also be a voltage overshoot when the voltage regulator tries to compensate for the inrush current.

Also, voltage regulators and speed governors are more stable when they have a load. First Energy's Eastlake and Avon Lake power plants have customers connected directly to the 13,200 volt generator buses as well as some 138 KV distribution substations that run directly off of the power plant. For instance, Brunswick, Ohio still had power on 14 August 2003 because their 138 KV was tapped in between Avon Lake's stepup transformers and the Fowler switchyard. When recovering from the blackout First Energy turned on some customers early partly to stabilize the generators, partly to absorb the charging current of the lines, and partly to absorb the bump that occurs when synchronizing to adjacent utilites.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources