Energising a 500kVA Tf from a 830 kVA Generator
|
Energising a 500kVA Tf from a 830 kVA GeneratorEnergising a 500kVA Tf from a 830 kVA Generator(OP)
Will the inrush current to the generator circuit breaker be less if there is a small load on the 500kVA transformer?
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: Energising a 500kVA Tf from a 830 kVA Generator
RE: Energising a 500kVA Tf from a 830 kVA Generator
Can you directly the transformer to the generator and avoid inrush by allowing the generator's AVR to bring the voltage up gently? If you switch on the other (HV? LV?) side of the transformer then you avoid inrush due to the transformer and make life easier for your generator. If you do this you should consider extending the generator's zone protection out to cover the transformer too.
----------------------------------
I don't suffer from insanity. I enjoy it...
RE: Energising a 500kVA Tf from a 830 kVA Generator
RE: Energising a 500kVA Tf from a 830 kVA Generator
Also, voltage regulators and speed governors are more stable when they have a load. First Energy's Eastlake and Avon Lake power plants have customers connected directly to the 13,200 volt generator buses as well as some 138 KV distribution substations that run directly off of the power plant. For instance, Brunswick, Ohio still had power on 14 August 2003 because their 138 KV was tapped in between Avon Lake's stepup transformers and the Fowler switchyard. When recovering from the blackout First Energy turned on some customers early partly to stabilize the generators, partly to absorb the charging current of the lines, and partly to absorb the bump that occurs when synchronizing to adjacent utilites.