I am using the Pile Supported Retaining Wall Example on Page 436 as a reference for a problem that I am working on.
Here are the loads I have about point A:
Sum V = 13.16 k
Sum H = 9.39 k
Sum M About Point A = 176.55 k-ft clockwise, (I have water pressures). With this type of loading my vertical resultant is near the edge of the toe, but still within the footing.
I am following the same pile layout right now, except I am using 5.5 ft spacing instead of 3 feet.
When I calculate the Vertical Components of Pile Reaction, I get a positive value for Row 1, a positive value for Row 2. BUT I get a negative value for Row 3.
Do you guys know what this negative value means? Also do you guys have an idea of what I can do to make this value positive?
THANKS
Sum V = 13.16 k
Sum H = 9.39 k
THANKS
RE: Pile Supported Wall - Foundation Engieering by Peck Hanson Thornburn
Appreciate your help.
TAHNKS
THANKS
Can you explain the safety factors a bit more. I was under the impression that we use FS=2. If we test a pile to the failing point, the pile capacity becomes the load at failure divided by 2. Can you please elaborate on the 2, 3 and the 6 safety factors.
On page 437 the following equation is being used for the Vertical Components of Pile Reactions:(Sum V/n) +/- (Sum M *d/ Sum d^2). Is the second term positive when "d" is to the left of C.G. and negative when "d" is to the right? I think there is more to it, but I can figuere it out since a vertical load is being calculated.
Appreciate Your Help
"Various published test results have indicated that the skin frictional resistance of piles to uplift loads is appreciably lower than that mobilied in resistance to compression loading. A reduction of 50% has been suggested for granular soils and the same order of reduction for long-term sustained loading for clays. . . . the appropriate safety factor should be applied to the skin friction values calculated by the methods described earlier . . . and if the uplift load on piles necessitates mobilization of skin friction approaching the ultimate values, it will be advisable to carry out uplift tests on selected full-scale piles to ensure that there is an adequate safety factor. . . jetty and wharf structures are subjected to lateral forces from berthing ships and from wave action. If these forces are transferred to supporting piles, the resutling lateral movement of the upper par tof the embedded length of the piles may destroy most of the skin friction . . . a generous factor of safety on the ultimate poull-out load should be adoped for piles carrying both lateral and uplift loads."
Usually one uses a SF of 3 (or 2.5 on piles) so my "suggestion" of 6 is the halfing of the skin friction loading based on skin friction/adhesion reduction. Of course, you can do tension tests to get more appropriate values. I've done this before and on timber piles we had 19 tons (vs 40 tons in compression - although the later would have included some base mobilization and was not loaded to failure).
I have that reference. Your statement is correct, but there's really not much more to it than that.
The equation used is simply P/A +/- Mc/I. This is simple statics. Looking at a vertical load,
Sum(V)/n is the P/A term.
Sum(M) * d/ Sum(d^2) is the Mc/I term; for piles, "I" is SUm(d^2), "c" is d.
To apply this equation, you must remember to keep your signs straight; a downward vertical load == positive (= compression in the pile) and upward load == negative (= tension in pile). When you define signs for the moment, counterclockwise moments == positive. the example uses distances defined as left of cg of pile group. Keep the correct sign on d as well.
Do the algebra, keep track of signs & it works. You'll note that for all rows, M is ccw = positive.
for row 1 M is positive, d is positive (row is left of cg of pile group), so Mc/I is positive, this is compression in pile.
for row 2, M is positive, d is negative row is right of cg of pile group), so Mc/I is negativel, this is tension in pile.
for row 3, M is positive, d is negative row is right of cg of pile group), so Mc/I is negativel, this is tension in pile.
Is this some help?
chichuck
That was very helpfull. Just one more quick question.
In the last section you mentioned:
for row 1, Mc/I is positive, this is compression in pile.
for row 2, Mc/I is negative, this is tension in pile.
for row 3, Mc/I is negative, this is tension in pile.
But the final results are:
Row 1: +22.7 k
Row 2: +21.9 k
Row 3: +21.0 k
So this means that all the piles in Row 1,2 and 3 are in compression?
THANKS
I meant that only the Mc/I portion is positive or negative, meaning compression or tension in the pile.
the P/A part (for piles, P/npiles) is always positive = compression.
P/A +/- Mc/I = total force in the piles. These are the numbers you refer to in your last reply; they are all positive so that meand all are compressive.
BTW, I looked over that example closely. I think the author has made an error. At the bottom of Sht.1 he calculates the resultant V, H and M loads on the pile group. H is correct. V is incorrect because it omits the value of Pv (the soil force acting vertically through point A; reference his example DP 26-1). M is incorrect because it only includes the eccentricity of the vertical load acting through the point at 0.83' from the cg of piles (and that is off by a little, as I said), but does not include the moment effect of the Ph acting at a height 5.33' above the piles. Correcting this, you would have a larger M than is shown in the example. Thus, the Mc/I term is larger for each pile. Some of the piles might actually have tension on them.
regards,
chichuck
I apologize for making two errors in my most recent reply.
1) the value of Ph from the figure given in HTP is actually zero, for flat backfill. His value of V is correcat.
2) he does in fact account for the fact that Pv is acting at 5.33' above pile group. He does this when he calculates the resultant of the vertical forces. So his value for M is also correct.
I've crafted a spreadsheet with the calculations necessary, including the ones that the book example omits with the words "similar to DP 26-1". that might make it more clear. I will post again with my website address when I have it up and available.
Sorry for the error.
chichuck
Look forward to seeing to spreadsheet to check my hand calcs.
THANKS
gman1
I got it posted and it appears to work now.
my website address is:
http://home.mn.rr.com/gbbadger/
download the spreadsheet hansen thornburn and peck.xls
regards,
chichuck
Got it. It was very helpfull. I had another quick question. I am looking at the possibility of using "one" big pile to support the loading, Is the approach in this example still appropriate, or is their other things I need to consinder.
THANKS
I think this example is not applicable to one big pile. With one pile, the entire load is resisted by that one pile, so the Mc/I portion of the calculation is not correct. I think one pile will resist the moment through some lateral soil resistance along the pile length. That is an entirely different case. I'm not sure how to analyze tha though.
Perhaps someone else on the forum can help.
chichuck
I still have not been able to find a pile supported retaining wall with one pile instead of multiple piles. Appreciate your help if you can point me in the right direction.
gman1
I had another,hopefully quick question. On this example Row 3 is 21k in compression. Say if instead Row 3 came out to be negative (tension), would that mean that I would have draw the line for Row 3 going down 21k on the diagram and then continue drawing three more lines at angle upward which would now add to -21k + 21.9K +22.7K + 22.7K = 46.3K, which indicates that SumV would have to be 46.3k on a 6' strip?
THANKS
gman1