Residual connected CTs and VTs

Residual connected CTs and VTs

Residual connected CTs and VTs

(OP)
Anyone pl. explain the pros and cons of residual connected current and voltage transformers to detect earth faults.
Advanced thanks...

RE: Residual connected CTs and VTs

Can you narrow down the question any at all?  What is your application, how is the system grounded, what are you doing, .....?

RE: Residual connected CTs and VTs

(OP)
Our site 11kV system has high resistance grounding system and used CBCT (Core balance current transformers) to detect the earth fault current. And 132kV system has solid ground system and here residually connected VT are used to find the earth fault (DEF).
I know residual connected CTs will be used for detecting solid ground system earth faults and CBCT will be used for detecting high resistance ground system earth faults. I would like to know the advantage of using residual connected VTs for detecting earth fault.If any specific advantage, pl. explain me
Thanking you.

RE: Residual connected CTs and VTs

If the 'D' in 'DEF' is directional, the residually connected VTs are the polarizing source for the directional element with the the actual tripping being done based on current.  The use of voltage tells nothing (or at least very little) about where the ground fault is located; it does an excellent job of indicating that the fault does exist, somewhere.

Zero sequence voltage says there is a ground fault somewhere, zero sequence current says that the fault current is flowing through the measuring point.

RE: Residual connected CTs and VTs

(OP)
Thank you Mr.Davidbeach. It is clear to me now.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources