Co Gen Trips on Neutral Current

Co Gen Trips on Neutral Current

Co Gen Trips on Neutral Current

(OP)
Hello,
   A job I did last year suddenly started having problems. It is a 600KW Co Generation unit at a hospital. The operating voltage is 480V. Everything worked fine for months and now it seems to be tripping on a "Neutral Current Fault". I don't have any more detail as I haven't been back to the site but everyone involved is stumped. Any idea what could cause this and what the resolution might be?

RE: Co Gen Trips on Neutral Current

Some new equipment in the hospital?  Anyone put a clamp or recorder on the neutral yet?

RE: Co Gen Trips on Neutral Current

Or new construction?

Bad connection in the neutral sensing?

RE: Co Gen Trips on Neutral Current

It seems solid earth and no isolation tranformer between utility supply and transformer. Check for any earth fault in system usually in lighting and also check neutral over current relay settings.

RE: Co Gen Trips on Neutral Current

One possible source  of neutral current in rotating equipment is an internal short to ground.  Is the generator bonded neutral to ground?

RE: Co Gen Trips on Neutral Current

(OP)
I don't have any new info other than some voltage and current readings the operators recorded. The internal short to ground is an interesting point. During the commissioning process the generator controls start up man closed the breaker 180 deg out of sinc. The generator just about lifted off it's mounts and blew some fuses in a 1200A switch. The alternator was inspected and we were told it was ok. Could this happening now be a result of this previous trauma? It happened about 5 months ago.

I don't believe there is any new equipment i the hospital and I have not been to the site to check any connections.

RE: Co Gen Trips on Neutral Current

Does the load vary, or the generator go on and off line?
The previous trauma may quite well have done damage that left the machine susceptable to further damage by thermal cycling.
I saw a coupling blown off of a 350 KW 1200 RPM by an out of sync. closure.  
yours

RE: Co Gen Trips on Neutral Current

If this generator is serving large motors, there is supposed to be a time delay on the transfer switch so that the motor slows way down before the switch makes.

Is this generator feeding the critical branch of the hospital?  I wouldn't want to be under the knife in a O.R.
with a generator tripping out.

RE: Co Gen Trips on Neutral Current

Just check whether the loads are balanced by measuring the phase current and monitor neutral current in the system. Also check neutral current high trip set.
Subramanian

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources