R-22 pressure vs temperature relation formula
Hi everybody,
Is there a formula we can use to get R-22 saturation temperature from the saturation pressure without using that ph table?
i need that formula in my contrl program.
thanks.
thanks.
RE: R-22 pressure vs temperature relation formula
ASHRAE Fundamentals, Chapt 17 has pressure enthalpy diagram and tables with everything you want to know about R22.
Took me less than 60 sec to get it
They were also published in the 1969 edition of ASHRAE's refrigerant "bible".
If you find any formula at Nist or Dupont, let me know, I couldnt.
Saturation Temperature t
need in Rankin
T = t + 459.69
Term 1 = A
Term 2 = B/T
Term 3 = C*LOG10(T)
Term 4 = D*T
Term 5 = (E*(F-T)/(F*T))*LOG10(F-T))
Saturated Vapour Pressure
psia = 10^(C8-C9-C10+C11+C12)
psig = psia - 14.696
Fixed Coefficients
A 29.35754453
B 3845.193152
C 7.86103122
D 0.002190939044
E 305.8268131
F 686.1