Speed of sound in two-phase mixture?
Guys do any of you know how to calculate the speed of sound in a two-phase mixture. Specifically this is steam of 65% quality at 1100 psig.
Obviously this puts me waaaay out of ideal gas assumptions. I can calc the c in the two phases but I am suspect of using a mass-wieghted average of the individual phase c, as one would do with enthalpy.
Any ideas?
Thanks!
Any ideas?
Thanks!
Thanks!
Pete
RE: Speed of sound in two-phase mixture?
I had a boss once that said "you can lacquer a turd and make it all shinny and pretty, but it is still a piece of crap". That may be too crass for this forum, but it has always meant to me that you shouldn't work any harder than the data will support.
David
C^2 =-V^2 dP/dV(isentropic) (1)
where C=sound speed, V=specific volume, P=pressure
Clearly,the specific volume,V and entropy, S should be known from
V=Vf+xVfg (2) where x is the quality
S=Sf +x Sfg (3)
The specific volume may be shown to be from Classus-Claperon (excuse spelling)
V=Vf + (S-Sf)dT/dP (4) Note S= constant
(Plot T vs P in the vicinity of your pressure and get first derivative. You will also have to plot dT/dP to get the second derivate.)
dV/dP=dVf/dP + (S-Sf)d^2T/dP^2 -dT/dP(dSf/dP) (5)
You now get dP/dv from (5) after a little graphical work.
Substitute in (1) and take the square root.
I have found it very interesting to try above for low quality steam water. See what happens as x approaches zero.
John
By the way to get dT/dP , note that dT/dP=Sfg/Vfg.
To get the second derivative, get Sfg/Vfg at a small increment of pressure (or temp)above and below (equal encrements)that of 1100 psig. That will give dT/dP at three points and numerically, one then obtains the second derivative.