KVA sanity check.

KVA sanity check.

KVA sanity check.

(OP)
Hello,
     Me and some of the colleagues are having a discussion about requesting electricty supplies from the Distribution Network Operator and stating the KVA rating of the supply.

The application is for street lighting, with the supply into a three phase feeder pillar, with circuits being supplied of individual phases.

Some of us are saying that the KVA rating should be calculated using the total current load from the three phases, and others are saying it should be done using the worse case loading on a phase?!

There doesn't seem to be a majority vote, so any help would be much appreciated to put our minds at rest.


Many Thanks.

RE: KVA sanity check.

Current in a three-phase system is always, with no exception, defined as current in one of the phases. So it seems very reasonable to use current in the heaviest loaded phase.

Gunnar Englund
www.gke.org

RE: KVA sanity check.

Agreed skogsgurra
And the current in the heaviest loaded phase is what will trip the circuit breaker, determine the wire size, and heat the transformer on that phase. The demand will be the total KVA, but use the heaviest phase loading for sizing the wire, the main breaker, and the transformers. I would hope that the lighting circuits can be balanced well enough that the question is acedemic.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources