Sensible Heat Load Question
Sensible Heat Load Question
(OP)
I am trying to determine the heat load in a clean room. The room has a t-bar ceiling with recessed flourescent lights. Does anyone know how much heat they will contribute to the room since they are recessed. I assume it is some percentage of power wattage of each unit. Alow was wondering how much heat is produced by the self powered hepa units which will be flush mounted in the ceiling. Possibly some percentage of the horse power or wattage requirement.





RE: Sensible Heat Load Question
RE: Sensible Heat Load Question
saludos.
a.
RE: Sensible Heat Load Question
Most important, you don't get this rejected heat for "free." It may not factor into the supplied cooling for the specific room, but it will show up as a coil load at the Air Handler.
Finally, if the space above the ceiling is not a return air plenum, then it does factor into the specific room load.
RE: Sensible Heat Load Question
HVAC68