Hi All,
We have a problem with a pressure transducer with a diaphragm isolater connected to an acid tank. The tank level varies from 10 - 100" (4-20mA). The problem is that the head pressure is so small that it takes a pressure change of around 20" for the diaphragm to move (jump) from convex to concave and vice versa.
This causes erroneous signals whenever the tank is emptying or filling.
I am looking for a diaphragm isolator that doesn't operate in this way, any help would be appreciated.
Barrie66

RE: Pressure Transducer

Hi, I would expect that you have a transducer with diaphragm seal, that there is a filling fluid between the transducer and the diaphragm. as such the diaphragm does not have this action (concave to convex).
If not then it is better to use one who have a filling sealed  fluid. Advise more details (model) of your P.Tx.

RE: Pressure Transducer

(OP)
Thank you AGomaa
We are using a Wika ECO-1 with fluid filled diaphragm seal.
What do you mean by "Have a filling sealed fluid?" I don't know this term.
Barrie66

RE: Pressure Transducer

The diaphragm seal I mean is a separate diaphragm seal typically used for aggressive media (acids etc.) this is not the diaphragm in the transducer.
A typical one is model 990.10. Normally you get the transducer and the diaphragm seal pre-installed and filled with seal.

Check with WIKA they should be able to identify the cause of the problem.
(Assuming that the fluid is water and transmitter is mounted at the bottom nozzle of tank):
I noticed that your working range is 0.025 to 0.249 bar your selected range is 0-1 bar that means at your 100% level you are operating at 25% of the tx range.

The transmitter range is
the 20" is =0.05 bar =5% of the tx range.

Check your installation where is the transducer mounted? It should be at the nozzle level, if below the nozzle then you will have + offset value.
I do not think that the range of this type of transducer can be changed.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources